How does an apartment become a 13D design?  13D is for single family and
duplexes. Am I missing something?

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: Karen Purvis [mailto:[email protected]] 
Sent: Wednesday, November 25, 2009 10:10 AM
To: [email protected]
Subject: RE: RE: concealed space

I went back and looked again an I was correct the first time, this will be
done as a 13D system.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David
Blackwell
Sent: Wednesday, November 25, 2009 1:02 PM
To: [email protected]
Subject: [!! SPAM] RE: concealed space

I sent a PDF of the table separately but it awaits moderator approval
due to exceeding its size...

 

David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David
Blackwell
Sent: Wednesday, November 25, 2009 12:57 PM
To: [email protected]
Subject: RE: concealed space

What George refers to is a very important aspect of the building code
that may be overlooked.  The architect's design choices can force you to
use a "higher" standard (NFPA 13 or NFPA 13R) system in the building
that otherwise falls within the scope of a "lower" standard (NFPA 13R or
NFPA 13D) system.

The (2006) IBC Code and Commentary Figure 903.3.1.1 contains a useful
table for understanding why an architect may specify a higher standard
than a sprinkler contractor may think is necessary.  

 

David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Wednesday, November 25, 2009 12:20 PM
To: [email protected]
Subject: RE: concealed space

And you can't use 13R under the 2006 IBC if the design team used the
sprinkler increase in order to build it, you can add a story but the SF
increase must come from frontage or other, non-sprinkler factors. Doubt
this
applies to YOUR building as it could also be under the Int'l Existing
Building Code. 

I'D BE AMAZED IF A SCHOOL CONVERTED TO APTS IS ABLE TO BE PROTECTED
APPROPRIATELY BY NFPA 13D !!!!!!!!  We've done 2 schools and a church
converted to apts in the past year, all 13R. There isn't a lot of
difference
in cost to do it correctly (13R) and if you need to, have em add some 8'
deep lintels where the living room ends and a corridor to bedrooms
start-
you'll not have to flow the corridor heads in that calc with the
living/dining/kitchen area. This can get you down to a 2 or 3 head calc,
max
4 in 13R. The little country church ended up as a 2-head flow, a
challenging
35 GPM at 30 PSI for a water supply- the developer had to change the
well
pump, big deal.

While you may find something on the AFSA site comparing 13r and 13D, the
text is available for free reading at www.nfpa.org codes and standards,
list
of codes and standards, click on 13r, applicable edition in your
jurisdiction, and then down at the bottom of the page, click on PREVIEW
THIS
DOCUMENT and fill out the questionnaire if you aren't logged in already.

David offers wise words WRT the IBC impact, although you likely don't
have
balconies in a school->apt conversion. 

To ALL my friends on the Forum, best wishes for a thoroughly enjoyable
thanksgiving respite.

George Church
Rowe Sprinkler


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to