Double check your NFPA 13D scope.  NFPA 13D is only applicable to
buildings which are: one-family dwellings; two-family dwellings; and,
manufactured homes.  Per the 2007 handbook commentary to NFPA 13D 1.1:
"...NFPA 13D is inappropriate for multifamily occupancies.  A
multifamily occupancy contains three or more dwelling units."

Apartments are normally designed to (at least) NFPA 13R, if not NFPA 13.

Note if the (2006) IBC is the applicable in the jurisdiction your
building is located, it affects the design of your sprinkler system.
Note that IBC 903.3.1.2.1 (for balconies and decks) requires more
sprinkler coverage than NFPA 13R requires; and, the requirements in IBC
903.4 may affect the choice of type of valve supervision used. 

 

David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Karen
Purvis
Sent: Wednesday, November 25, 2009 8:52 AM
To: [email protected]
Subject: concealed space

I have checked the archives and can not find what I am looking for. I
have
an old school building with an attic area that is not accessible and a
6'
crawl space with no equipment. Building is all wood. They are redoing
the
building into apartments (13D). For some reason I remember someone
telling
me or reading that in a 13R or 13D system if the areas mentioned were
net
being used or accessed then they did not need to be sprinkled. Is this
something I dreamed up?

 

Karen Purvis

Senior Designer

Facility Systems Consultants

713 South Central Street,

Suite 101

Knoxville, TN 37902

ph.865-246-0164

fax 865-246-1084

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to