And I don't disagree with Ron on second read.   Was in a grueling meeting all 
morning and didn't read closely enough; electric water heater ...  no sprinkler 
required.

Disclaimer ...  my opinion ... yada, yada.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: Ron Greenman [mailto:[email protected]] 
Sent: Wednesday, November 25, 2009 11:42 AM
To: [email protected]; Steve Leyton
Subject: Re: 13D 8.6 Question

I'll disagree with Steve. Room is less than 24 sqft, not greater than
3 ft in the least dimension and does not contain a fuel fired
appliance. Plus it is accessed from the outside so even though it is
within the rectangular perimeter of the structure it is essentially an
exterior closet. And even if it were accessed from inside I'd say it
meets the spirit of those small exempt spaces.

On Wed, Nov 25, 2009 at 10:57 AM, steve <[email protected]> wrote:
> Not IMHO.
>
> Not a formal interp, my opinion only, yada, yada, yada.
>
>
> Sent from my Verizon Wireless BlackBerry
>
> -----Original Message-----
> From: "Mike Cabral" <[email protected]>
> Date: Wed, 25 Nov 2009 10:46:01
> To: <[email protected]>
> Subject: 13D 8.6 Question
>
> A Manufactured Home (FEMA trailer 14' x 60') has an equipment room that 
> contains a electric hot water heater. Area of the room is six (6) total 
> square feet. Least is dimension 2'. No access from inside the unit. The space 
> has an access panel on the outside of the unit. It has a wood floor with ½" 
> sheetrock walls and ceilings. Can the sprinkler be omitted from this space?
> Mike Cabral
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> <http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
> For Technical Assistance, send an email to: [email protected]
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> __________ Information from ESET NOD32 Antivirus, version of virus signature 
> database 4636 (20091125) __________
> The message was checked by ESET NOD32 Antivirus.
> http://www.eset.com <http://www.eset.com>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4636 (20091125) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4636 (20091125) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to