Jim,

It's been awhile since I last looked at this issue, but if I remember
correctly this is only an issue when the ceiling assembly is not braced to
resist movement.  Ceilings that incorporate lateral force bracing are exempt
from the oversize escutcheon requirement.  So, if the ceiling assembly is
not properly braced, the oversized escutcheon is required.

 

Here is a link to a good tech guide that might help,
http://www.nwcb.org/images/resource_files/401%20Suspension%20Systems%20for%2
0Acoustical%20Lay-in%20Ceilings(2009).pdf

 

 

Bob Knight

 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Friday, December 04, 2009 2:26 PM
To: [email protected]
Subject: Clearance for Drops

 

Good Friday Afternoon All!!

 

 

 

Does anybody no if there is a clearance (annular) requirement for drops thru

hard lids or suspended ceilings?  I had a Fire Marshal call me this morning

regarding this issue and oversize escutcheons to fill the void, I am not

aware of this requirement.  I have looked in the IBC Chapter 16, is it in

ASCE7?  What do the Californians know about this?

 

 

 

Thanks in advance, and all have a great weekend.

 

 

 

Jim Johnston, P.E.

 

Fire Protection Engineer

 

Inland Fire Protection, Inc

 

1100 Ahtanum Road

 

Yakima, WA 98903

 

Phone 509-248-4471

 

Fax 509-248-1180

 

[email protected]

 

 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 

For Technical Assistance, send an email to: [email protected]

 

To Unsubscribe, send an email to:[email protected]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to