Ken, Good point there about the decks but I think the logic still holds if you remove that bit of distraction from my argument. Let me try again. Since 13 addresses chutes to re-iterate it in IBC and then direct you to 13, 13R or 13D depending on type of occupancy would then be redundant if the IBC chute rule were to only apply to 13. Bottom line for me is that I'm reading this to mean any trash chute in any building. Around these parts we also see self-closing fire doors (for lack of a better term) at the bottom of these chutes so a dumpster fire will fuse a link releasing the "door" and sealing the dumpster from the shaft. These things make really nice chimneys that vent to each floor of a building.
On Wed, Dec 16, 2009 at 3:03 PM, Ken Holsopple (forum) <[email protected]> wrote: > Ron, > > I think I am going to disagree with some of your statements. Section 6.7.2.1 > tells me what I need to refer to 13 for. That would be design discharge, # > of design sprinklers, sprinkler coverage, and position of sprinklers. These > are the only things I should be looking back in to 13 for. > > Keep in mind the Type V deck coverage requirement is listed directly > underneath the 903.3.1.2 in IBC (06) > > Ken > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Ron Greenman > Sent: Wednesday, December 16, 2009 4:37 PM > To: [email protected] > Subject: Re: IBC and NFPA 13R - Linen/Trash Chutes > > I think all you have to do is follow the hierarchy path. The chute > requirement is in addition to the requirements of 13R wherever 13R > allowed. This is the same as the requirement for protecting the decks > even though they are outside of the building and therefore outside the > scope of 13 (except where required and then that's to 13). And I'd say > the chute needs to meet 13 since it is out of the occupied space. > Rationale would be that because 13R is for life safety only (as > demonstrated by the exemption of all non-occupied spaces) and the > chute is an unoccupied space that must be protected you then need to > fall back to the non-occupied but required space clause in 13R that > requires designing such areas to 13. > > On Wed, Dec 16, 2009 at 1:12 PM, Ben Young <[email protected]> > wrote: >> John, >> >> When you put it in terms of vertical communication of fires, it does make >> more sense, especially when talking about an apartment or other building > of >> that type. >> >> But if I'm understanding what you all have said, it seems that according > to >> the IBC, if you turned a single family detached dwelling into a board and >> care facility, a laundry chute in that house would then require sprinkler >> protection. >> >> Is that correct? >> >> On Wed, Dec 16, 2009 at 3:35 PM, John Drucker > <[email protected]>wrote: >> >>> Ken, >>> >>> Yes the chute and the terminal rooms require sprinkler protection >>> regardless of whether the building is suppressed. Use R under the IBC is >>> always required to be suppressed so it's a mute point but more >>> importantly the Chapter 7 requirement is addressing a target hazard, >>> i.e. fires in chutes and rooms and or closets serving the chute and not >>> the building itself. IBC 707.13.6. being a subsection of Refuse and >>> Laundry Chutes prescribes automatic sprinkler protection. IBC 903.2.10.2 >>> merely tells you where to put the sprinklers, i.e. top, terminal rooms >>> and alternate floors when the chute extends three or more floors. The >>> section also prescribes service access for the sprinklers. >>> >>> The exceptions contained in 13R, or for that matter any other standard >>> are not applicable since the building code trumps the standard. >>> >>> Hope that helps, >>> >>> John Drucker Jr CET >>> Fire Protection Subcode Official >>> Fire/Building/Electrical Inspector >>> Borough of Red Bank, NJ >>> >>> -----Original Message----- >>> From: [email protected] >>> [mailto:[email protected]] On Behalf Of Ken >>> Holsopple (forum) >>> Sent: Wednesday, December 16, 2009 2:43 PM >>> To: [email protected] >>> Subject: IBC and NFPA 13R - Linen/Trash Chutes >>> >>> Folks.....I need some opinions.... >>> >>> I have multiple buildings that fall into a Group R category and also >>> qualify for the use of NFPA 13R. These buildings all have either trash >>> or linen chutes. The IBC (2006) states the following.... >>> >>> 707.13.6 Automatic sprinkler system. >>> An approved automatic sprinkler system shall be installed in accordance >>> with Section 903.2.10.2. >>> >>> 903.2 Where required. >>> Approved automatic sprinkler systems in new buildings and structures >>> shall be provided in the locations described in this section. >>> >>> 903.2.7 Group R. >>> An automatic sprinkler system installed in accordance with Section 903.3 >>> shall be provided throughout all buildings with a Group R fire area. >>> >>> 903.2.10.2 Rubbish and linen chutes. >>> An automatic sprinkler system shall be installed at the top of rubbish >>> and linen chutes and in their terminal rooms. Chutes extending through >>> three or more floors shall have additional sprinkler heads installed >>> within such chutes at alternate floors. Chute sprinklers shall be >>> accessible for servicing. >>> >>> 903.3.1.2 NFPA 13R sprinkler systems. >>> WHERE ALLOWED in buildings of Group R, up to and including four stories >>> in height, automatic sprinkler systems shall be installed throughout in >>> accordance with NFPA 13R. >>> >>> NFPA 13R Section 6.8.5 >>> Sprinklers shall not be required in attic....elevator machine >>> rooms....elevator shafts......and other concealed spaces not intended >>> for living purposes or storage and do not contain fuel fired equipment. >>> >>> With the sections noted above I am thinking that the blanket statement >>> that IBC is trying to make is that sprinklers are required in any >>> linen/trash chute whether the building has a fire sprinkler system or it >>> doesn't. >>> However, I am of the opinion that if I meet the qualifications for a >>> building to use the NFPA 13R standard then 903.3.1.2 acts as an >>> exception to the previous rules in the "where required" section. Anybody >>> else see it this way? >>> >>> I am having a hard time accepting that I don't need sprinklers in an >>> elevator pit or elevator machine room (ya know flammable hydraulic >>> fluid?), but make sure you protect the discarded Sara Lee pie pans (that >>> can't be used as heat collectors anymore) or Aunt Ethel's stinky socks. >>> >>> Is everybody lost but me again????? >>> >>> Best Regards and Happy Holidays, >>> >>> Ken Holsopple >>> >>> >>> >>> >>> >>> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >>> >>> For Technical Assistance, send an email to: [email protected] >>> >>> To Unsubscribe, send an email >>> > to:[email protected]<to%3asprinklerforum-requ...@fire > sprinkler.org> >>> (Put the word unsubscribe in the subject field) >>> >>> >>> CONFIDENTIAL AND PROPRIETARY: >>> This email message is intended only for the use of the individual or > entity >>> to which it is addressed and may contain information that is privileged > and >>> confidential, nor is it, unless specifically stated, intended to be > relied >>> upon by any person or persons other than the individual or entity named >>> above and no warranties or representations are made or intended to > persons >>> or entities not named above. If the reader is not the intended > recipient, >>> you are hereby notified that any dissemination, distribution or copying > of >>> this communication is strictly prohibited. If you have received this >>> communication in error, please notify us immediately by telephone, return >>> this message to the address above and delete all copies. Thank you. >>> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >>> >>> For Technical Assistance, send an email to: [email protected] >>> >>> To Unsubscribe, send an email > to:[email protected]<to%3asprinklerforum-requ...@fire > sprinkler.org> >>> (Put the word unsubscribe in the subject field) >>> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email to:[email protected] >> (Put the word unsubscribe in the subject field) >> > > > > -- > Ron Greenman > Instructor > Fire Protection Engineering > Bates Technical College > Tacoma, WA > > Member: > SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)