Warm wet air being compressed to hot wet air in the valve room and
then being pushed into cold pipes. What you describe is a regular
thing here in the Pathetic Northwet.

On Fri, Jan 8, 2010 at 3:09 PM, Mark Sornsin <[email protected]> wrote:
> I suspect your second example is what's happening - the system piping is only 
> 5 yrs old and they claim the compressors don't run much (never ran for the 
> 1/2 hour I was there - for whatever that's worth).  Except, they 'reportedly' 
> drained the drum 8 or 10 times over a few months and still get this much 
> water. Seems remarkable.
>
> Mark
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Chris Cahill
> Sent: Friday, January 08, 2010 4:24 PM
> To: [email protected]
> Subject: RE: Excessive Condensate
>
> Yep and many times it's due to a leaky system where the compressor runs a
> lot.  Put a 40 psi test on the system to see how tight it is.  That will
> confirm whether this is new water or from the past trip.
>
> I've also see a cycle where the DD wasn't drained in fall and they have a
> freeze up in a DD.  Then a couple week later another.  What's happening
> there is the first trip adds water and some of it freezes to the inside of
> the pipe.  Then a few weeks later with weather changes it melts and collects
> in the DD only to freeze during the next cold snap and so the cycle starts
> again.
>
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>
> 763-658-4483
> 763-658-4921 fax
>
> Email: [email protected]
>
> Mail: P.O. Box 69
>        Waverly, MN 55390
>
> Location: 4439 Hwy 12 SW
>              Waverly, MN 55390
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Mark Sornsin
> Sent: Friday, January 08, 2010 3:59 PM
> To: '[email protected]'
> Subject: Excessive Condensate
>
> I have a client with a parking garage.  Large enough for two dry-pipe
> systems.  Each are piped relatively flat (pitched per NFPA 13, but no more);
> each on a big loop of 4 in main with side feed branch lines out the side of
> the mains.
>
> This system was last flooded last summer (say August).  Since that trip test
> and subsequent draining, the client  has blown out all 6 low point drum
> drips twice a month, every month. But even still, over Christmas, and only
> two weeks after blowing out the drum drips, they froze 4 of the 6 drum drips
> to the point of breakage - 3 of the 6 were filled with ice throughout the 2
> in. x 12 in. drum, and up the 5 or 6 ft. of 1 inch pipe.
>
> The contractor that replaced the drum drips noted that there was no
> appreciable water on top of the dry valves, so the water in the pipes
> appears to be entirely from condensate.  Or maybe, somehow, residual from
> the trip testing 5 months ago (???).
>
> Has anyone of you seen this amount of condensate coming from a dry system?
> The air compressors are floor mounted with no tank. The riser room is
> somewhat damp (large sump pit located here, too) and maintained at about 55
> degrees.  But I still have a hard time imagining how that much water could
> come from condensate.
>
> Any thoughts?
>
>
> Mark A. Sornsin, PE
> Fire Protection Engineer
> Ulteig Engineers, Inc.
> Fargo, ND
> Direct:    701. 280.8591
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to