Where does it say you calc only one system at a time. Not only you SHOULD
but you HAVE to calc the entire design area. If it comes from more than one
system, that is what you have to do. Some time back I was reviewing a design
that had several deluge systems, but no walls between them. The designer
calcd. one system at a time, and it got installed. I got to review it only
after the installation. What would happen if a fire happened at the boundary
of two systems. Then both systems would go off. A wet and pre-action won't
be as drastic as 2 deluge systems, but still the hydraulically most
demanding may be at the boundary. 

Tony  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: January 13, 2010 2:20 PM
To: [email protected]
Subject: RE: mixed systems

I don't think we need more info.  The code doesn't say anything, it's
perfectly fine.  Want to play games put every other line on a different
system.  Sprinkler code doesn't even require separations of any kind unless
using a room design method. Building Code separations are beyond us
contractors pay grade. 

And remember you only are calc'ing on system at a time.  Yes a design
density may have to extend 15' beyond to another system but you still only
calc one system at a time.  What might be interesting is say a 500 sq.ft. PA
system within a regular wet.  Technically you don't have to calc the extra
1,000 sq.ft. on the wet but you should. 

Now if she is questioning the EOR then more info is still not important nor
is the code one way or another. The EOR doesn't need a reason,
unfortunately.  

Craig's follow up comments are certainly relevant to the FPE'ing but still
not related to the question does the code say no to splitting how ever you
want. Smoke issue could be addressed (DIPA), wetting electrical stuff (PA
with 20' overhang), oiled filled transformers might change the density but
not an issue with splitting a system however you want.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, January 13, 2010 2:59 PM
To: [email protected]
Subject: RE: mixed systems

We need more info on what's going on and why.   


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Karen Purvis
Sent: Wednesday, January 13, 2010 2:55 PM
To: [email protected]
Subject: mixed systems

Where in the code does it say that you cannot mix systems in an area. In
other words if I have a large room that a section of the room is separated
by a chain link fence and one side has a wet system and the other side needs
a preaction system. Where does it tell me I can't do that? 

 

Karen Purvis

Senior Designer

Facility Systems Consultants

713 South Central Street,

Suite 101

Knoxville, TN 37902

ph.865-246-0164

fax 865-246-1084

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________