Chris,
I still think that if the hydraulically most demanding area falls either
between 2 systems or branch lines off 2 separate cross mains, you still
need to pick up the full remote area for the area/density method.  The
fire will not know what sprinklers are supplied from which pipe.  You
still must pick up the " hydraulically most demanding area".
Dewayne

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Wednesday, January 13, 2010 4:41 PM
To: [email protected]
Subject: RE: mixed systems

'02 Chapter 14.4.4 Calculation Procedure in many sections talks about
systems. 

14.4.4.1 - For all systems the design area shall be the hydraulically
most demanding...

14.4.4.1.1.1 - Where the design is based on the density/area
method...inclusion of sprinklers on both sides of the cross main.

14.4.4.1.1.3...the design area shall be extended to include sprinklers
on adjacent branch lines supplied by the same cross main.

Looks to me if you follow the procedure you can never get to another
system or even a different set of BL's supplied from different CM on the
same system.  This can be used in designs.  Add a CM to shorten the BL's
which might be driving higher pressures.  Not common I know but
acceptable. We do it in really big cold boxes where grids are not
allowed.  

11.2.3.1.8 (1) or (2) provides for areas of sprinkler operation less
than the normal 1500 or 2500.  

I see your point in a deluge.  I don't think I ever was involved with a
deluge to speak from experience.  Ch. 14.4.4 only applies to the area
density designs out of ch.11 and ch.12.  I don't think deluge would use
this chapter for the calc procedures because I don't see deluge designs
in ch.12 or ch.11.  14.6 seems to say go elsewhere.  What would you do
where 4 systems came together at a single point?  That's a lot of
water...and maybe rightfully so according to the applicable standard
which isn't 13. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Wednesday, January 13, 2010 3:50 PM
To: [email protected]
Subject: RE: mixed systems

Where does it say you calc only one system at a time. Not only you
SHOULD but you HAVE to calc the entire design area. If it comes from
more than one system, that is what you have to do. Some time back I was
reviewing a design that had several deluge systems, but no walls between
them. The designer calcd. one system at a time, and it got installed. I
got to review it only after the installation. What would happen if a
fire happened at the boundary of two systems. Then both systems would go
off. A wet and pre-action won't be as drastic as 2 deluge systems, but
still the hydraulically most demanding may be at the boundary. 

Tony  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: January 13, 2010 2:20 PM
To: [email protected]
Subject: RE: mixed systems

I don't think we need more info.  The code doesn't say anything, it's
perfectly fine.  Want to play games put every other line on a different
system.  Sprinkler code doesn't even require separations of any kind
unless using a room design method. Building Code separations are beyond
us contractors pay grade. 

And remember you only are calc'ing on system at a time.  Yes a design
density may have to extend 15' beyond to another system but you still
only calc one system at a time.  What might be interesting is say a 500
sq.ft. PA system within a regular wet.  Technically you don't have to
calc the extra 1,000 sq.ft. on the wet but you should. 

Now if she is questioning the EOR then more info is still not important
nor is the code one way or another. The EOR doesn't need a reason,
unfortunately.  

Craig's follow up comments are certainly relevant to the FPE'ing but
still not related to the question does the code say no to splitting how
ever you want. Smoke issue could be addressed (DIPA), wetting electrical
stuff (PA with 20' overhang), oiled filled transformers might change the
density but not an issue with splitting a system however you want.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, January 13, 2010 2:59 PM
To: [email protected]
Subject: RE: mixed systems

We need more info on what's going on and why.   


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Karen
Purvis
Sent: Wednesday, January 13, 2010 2:55 PM
To: [email protected]
Subject: mixed systems

Where in the code does it say that you cannot mix systems in an area. In
other words if I have a large room that a section of the room is
separated by a chain link fence and one side has a wet system and the
other side needs a preaction system. Where does it tell me I can't do
that? 

 

Karen Purvis

Senior Designer

Facility Systems Consultants

713 South Central Street,

Suite 101

Knoxville, TN 37902

ph.865-246-0164

fax 865-246-1084

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to