If I'm remembering it correctly the statement was that someone had them
calc. the area between two "Deluge" systems that were not separated by walls
on the assumption that a fire in that area would set off both systems at the
same time. This is similar to NAVFAC hangers with Deluge systems where we've
had to prove the most demanding two adjacent systems flowing at the same
time. I believe that deluge systems, open head foam systems or other special
hazard systems (Non-Segregated Gas systems) may be the only cases where the
flow thru 2 systems is a greater demand than one, since the remote area is
not a square footage, but the entire system. 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


Subject: RE: mixed systems

Thanks Roland,

Subject: Re: mixed systems

Anyone want to venture a guess on whether water flowing through 2 systems is
more or less hydraulically demanding than that flowing through one?  