The way I understand it 40,000 sf is your limit. * 8.2.1 *The maximum floor area on any one floor to be protected by sprinklers supplied by any one sprinkler system riser or combined system riser shall be as follows: (3) Extra hazard (a) Pipe schedule — 25,000 ft2 (2323 m2) (b) Hydraulically calculated — 40,000 ft2 (3716 m2) (4) Storage—High-piled storage (as defined in 3.9.1.13) and storage covered by other NFPA standards — 40,000 ft2 (3716 m2)
*3.9.1.13 *High-Piled Storage. Solid-piled, palletized, *rack storage*, bin box, and shelf storage in excess of 12 ft (3.7 m) in height. -Jim On Thu, Jan 14, 2010 at 11:48 AM, Fletcher, Ron <[email protected]>wrote: > We have 65,000 sqft of rack storage that requires in-rack sprinklers. > The racks span an area that is protected by 4 roof systems. Can we use a > single system to supply the in-rack and have all 65,000 sqft on a single > valve? > > I thought that I read somewhere once upon a time that in-rack systems > had to be zoned similar to roof systems i.e. 40,000 sqft max etc... > > Ron Fletcher > Aero Automatic > Phoenix, AZ > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)