Please note I am not arguing the big picture.  One really, really should
calc the most demanding area no matter how many systems it may or may not
cross.  

My point was the standard was deficient in really small systems within the
area of a larger system.  Even if the area is bound by walls it only helps
IF the walls and openings meet the room design criteria.  And if it's EH or
storage there are no walls in the standard that are clear to use the room
design method. 

Your small building example would be a hard sell in a court arrangement when
the judge asked the Fire Marshal exactly where did the defendant not follow
the procedure set forth in the standard.  Of course the defendant in that
case would have a hard sell to the jury if there was a fire and a loss in
either property or life.   

If that's what was added to the '10 I still think it's deficient.  First
this belongs in the body of the standard not the annex.  Second it doesn't
address Karen's situation neatly.  It seems more geared to really small
buildings and not really small systems in otherwise big buildings.  

And third and most important IMHO typically is a bad choice of words.
Typically by it's definition allows for atypical.  Thus the latest and
greatest edition provides for "The area of sprinkler operation 'does not
always but usually' (atypically) encompasses enough of the floor area to
make-up the minimum allowed (should be required) size of the remote area up
to the entire area of a single floor of the building".  Even changing
typically to should IMHO would have made for a clearer intent.  And I'm not
even arguing the intent is anything other than full remote areas.  

I know I'm parsing words but this is how the cheaters survive and the
lawyers make a buck.  That's the real world we fight against.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Thursday, January 14, 2010 9:52 AM
To: [email protected]
Subject: RE: mixed systems

Thanks Roland,
I guess I wasn't that clear in my statement but my thoughts were along
the lines of the annex material you pointed out.
Dewayne   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, January 14, 2010 9:39 AM
To: [email protected]
Subject: Re: mixed systems

Anyone want to venture a guess on whether water flowing through 2
systems is more or less hydraulically demanding than that flowing
through one?  Granted you could have a case where a higher hazard in a
relatively small area is centered between systems that MIGHT be more
demanding with two flowing but until I see the numbers, I'm not going to
pick the fly**** out of that pepper. The calc applies to one system.
Having said that the criteria as Chris pointed out is a tad loose and
leaves it open for SMALL systems.  Case in point, you have a 1,500 sf
building and really bad water.  One might consider putting in two system
at 750 sf each and claim that is the size of the remote area since it is
the entire system.  I had this exact issue before this cycle and after
butting heads over it can say the text did not cover that situation. It
does now in the Annex of 2010 in A. 
11.2.3.1.4(1) where it states:

  The area of sprinkler operation typically encompasses enough of the
floor area to make-up the minimum allowed size of the remote area up to
the entire area of a single floor of the building

Roland



On Jan 14, 2010, at 4:30 AM, Dewayne Martinez wrote:

> Chris,
> I still think that if the hydraulically most demanding area falls 
> either between 2 systems or branch lines off 2 separate cross mains, 
> you still need to pick up the full remote area for the area/density 
> method.  The fire will not know what sprinklers are supplied from 
> which pipe.  You still must pick up the " hydraulically most demanding

> area".
> Dewayne

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to