Where does it say you calc only one system at a time. Not only you SHOULD
but you HAVE to calc the entire design area. If it comes from more than one
system, that is what you have to do. Some time back I was reviewing a design
that had several deluge systems, but no walls between them. The designer
calcd. one system at a time, and it got installed. I got to review it only
after the installation. What would happen if a fire happened at the boundary
of two systems. Then both systems would go off. A wet and pre-action won't
be as drastic as 2 deluge systems, but still the hydraulically most
demanding may be at the boundary. 

Tony  