When you look at 8.9.5.1.3, you'll not the Max. soffit distance below the head is 14" if the head is 17'> away. Ok this pretty well limits it what's max head coverage? 16x20 room, So we pick a K5.8 TYCO TY4334 155'F and mount it 12" down. If the face of our soffit is 17'+ away from the head the soffit could be up to 26" down from the ceiling. But if the soffit is > than 26" then you need a head under the soffit.
Same head same room, head at 6" down from ceiling, soffit 17'+ away bottom of soffit could be up to 20" down from the ceiling. If the soffit is > than 20" down you need a head under it. Remember that the wall the soffit is on can still be no greater than 20' from the head. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)