Your mechanical, janitor, and recycling rooms don't have a barrier or
partition capable of delaying heat from a fire in those rooms from fusing
sprinklers in the corridor or bathrooms, etc.? 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Hinson, Ryan
Sent: Wednesday, March 03, 2010 9:52 AM
To: '[email protected]'
Subject: Adjacent hazards

NFPA 13(2010) section 11.1.2(1) states "Where areas are not physically
separated by a barrier of partition capable of delaying heat from a fire in
one area from fusing sprinklers in the adjacent area, the required sprinkler
protection for the more demanding design basis shall extend 15 ft beyond its
perimeter."  The appendix gives a storage example.  My question is:  Is the
spacing of the more demanding basis also to be extended that 15 ft for an OH
scenario into a LH area through non rated walls?  In other words, do I have
to protect light hazard corridors or bathrooms with 130 sq ft max sprinkler
spacing since they are within 15 ft of mechanical, janitor, and recycling
rooms?  It seems like overkill to me to have to space heads in a portion of
a corridor or bathroom at 130 sq ft unless there are rated walls separating
them from the other hazards.  Thoughts?

Thank you,

Ryan L. Hinson, EIT, NICET III
Fire Protection Systems Designer, Aviation and Facilities Group
Minneapolis-St. Paul Office
Burns & McDonnell
8201 Norman Center Drive, Suite 300
Bloomington, MN 55437
Direct: 952-656-6003 Ext 3662
Fax: 952-229-2923
www.burnsmcd.com<BLOCKED::www.burnsmcd.com>


Proud to be one of FORTUNE's 100 Best Companies To Work For

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to