I misunderstood a superior and was looking for clarification.  Thank you.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662
-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Wednesday, March 03, 2010 9:58 AM
To: '[email protected]'
Subject: RE: Adjacent hazards

If your walls extend to the bottom of the deck/ceiling, then you are physically 
separated and do not need to extend the higher hazard 15'.

Look at that, an AHJ CAN get it right!

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487


-----Original Message-----
From: Hinson, Ryan [mailto:[email protected]] 
Sent: Wednesday, March 03, 2010 10:52 AM
To: '[email protected]'
Subject: Adjacent hazards

NFPA 13(2010) section 11.1.2(1) states "Where areas are not physically 
separated by a barrier of partition capable of delaying heat from a fire in one 
area from fusing sprinklers in the adjacent area, the required sprinkler 
protection for the more demanding design basis shall extend 15 ft beyond its 
perimeter."  The appendix gives a storage example.  My question is:  Is the 
spacing of the more demanding basis also to be extended that 15 ft for an OH 
scenario into a LH area through non rated walls?  In other words, do I have to 
protect light hazard corridors or bathrooms with 130 sq ft max sprinkler 
spacing since they are within 15 ft of mechanical, janitor, and recycling 
rooms?  It seems like overkill to me to have to space heads in a portion of a 
corridor or bathroom at 130 sq ft unless there are rated walls separating them 
from the other hazards.  Thoughts?

Thank you,

Ryan L. Hinson, EIT, NICET III
Fire Protection Systems Designer, Aviation and Facilities Group
Minneapolis-St. Paul Office
Burns & McDonnell
8201 Norman Center Drive, Suite 300
Bloomington, MN 55437
Direct: 952-656-6003 Ext 3662
Fax: 952-229-2923
www.burnsmcd.com<BLOCKED::www.burnsmcd.com>


Proud to be one of FORTUNE's 100 Best Companies To Work For

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to