Doesn't the main have to be pitched?

8.15.2.3.1 Dry Pipe Systems in Non-Refrigerated Areas. In dry pipe 
systems branch lines shall be pitched at least 1⁄2 in. per 10 ft (4 
mm/m) and mains shall be pitched at least 1⁄4 in. per 10 ft (2 mm/m).

I think the contractor was confused between preaction and dry systems. 
It used to be that a preaction system in a heated area did not have to 
be pitched. However, as long as I can remember, dry systems have been 
pitched.

On 3/14/2010 1:57 PM, Jay Jay Blocker wrote:
> I have a scenario I would like some input on.  We have a property with five 
> buildings all five buildings are five stories tall with dry systems in the 
> attics.  4 inch schedule 10 main with Tyco attic heads on 1.25 inch sprigs.  
> 4 of the buildings have all the main and sprigs in the attic with only the 
> supply and the drum drips in the heated floor below.  Building five has the 4 
> inch main hung in the hall way below with 10 foot sprigs penetrating the 
> rated ceiling into the attic.  NO pitch on any of the main.  I have not  seen 
> a dry system done this way before but can not seem to find anything that says 
> it cant be done this way.  (13-2002)  Any input on this arrangement?
>
> The issue I am having is the 4 inch pipe is developing pinhole leaks at only 
> 18 months of service.  Upon replacement of a section of pipe a sludge about 1 
> inch thick was discovered as well as large amounts of water.  I know the 
> pitching will correct the draining of the water but our concern was where the 
> water was coming from.  The installing contractor told the customer "Idid you 
> a favor to keep your main from freezing."  The question was asked if it was 
> possible that all the sprigs being in the cold area and the main in the dry 
> could be the cause for the excess water (condensation).  Also is there any 
> place I can send a sample of the sludge to get it tested for possibility of 
> MIC?
>
> Thanks for the help.
>
> Jeremy Blocker
> EFPS
> (303) 353-9712
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>    
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to