Jay,
Back in march you were fighting a MIC problem and was going to research some
different labs.
Would you care to share your results?
You can contact me off line if you prefer.

Thank you for your attention.
Andy Johnston
Your are welcome to call my Cell (386)547-4970
 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay Jay
Blocker
Sent: Monday, March 15, 2010 10:01 PM
To: [email protected]
Subject: Re: MIC

Thanks for the help on this, I am going to be requesting sample reports from
atleast four companies now.  I was still wondering if anyone had ever seen
this particular pipe arrangement with regard to the main in the hall
and sprigs in the cool area?  Because of cramming the main into the 18
inches of available space above grid and below fire barrier there was
not enough room to slope the piping is what the installing contractor
says.  Would that not then mean it could not meet the requiremnts of
8.15.2.3.1 that this particular arrangement of piping would not have been
advised?
 
J. Blocker
EFPS