Reliable makes extended escutcheon plates (OOPS plateY for that purpose that fit over both friction fit escutcheons and cover plates for our sprinklers. These escutcheons are for aesthetic purposed only and do notr have to be part of any listed escutcheon assembly. Check the product solutions section of our website to see if the inner dimension will fit the sprinkler escutcheon you are using.
Regards, Salvatore Izzo PE SFPE Mgr-Reliable Tech Services Sent from my Verizon Wireless BlackBerry -----Original Message----- From: Randy Knutson <[email protected]> Date: Fri, 19 Mar 2010 13:52:08 To: [email protected]<[email protected]> Subject: Over sized escutcheon for seismic clearances Forum Members, On one of our projects, we have to maintain a 2" clearance between the Armstrong ceiling tile and the sprinkler assembly. Do the escutcheon plates that cover this bigger hole have to be listed? We are using Tyco TY-FRB SSP's with recessed escutcheons and I don't see that Tyco manufactures an expansion plate. Any help would be appreciated. Randy Knutson, CET Sales Manager Shilo Automatic Sprinkler, Inc. 208-466-0006 ext 119 208-466-7890 fax _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)