I believe you only have to use the big hole and the big escutcheon when the ceiling isn't seismically qualified (braced and with tiles clipped in. Since it's the lack of bracing for the ceiling that's making the problem why not have the ceiling guy do his job since ceilings in seismic zones have to meet their seismic requirements. Why is the owner's building always our problem (not strong enough to hold our stuff up or moves too much in a seismic event) when isn't built correctly?
On Fri, Mar 19, 2010 at 12:02 PM, ParsleyConsulting <[email protected]> wrote: > Sal, > > I wonder if a listing is required for the escutcheon Randy is referring > to is required, since it is to be provided for something other than > aesthetics, such as providing protection for the sprinkler head through > a ceiling. The provision for clearance is coming from a section of > ASCE7. I don't know if testing is required to confirm that the > requisite clearance is provided or how the clearance from such an > escutcheon would function in a seismic event. > > Has there been any information transmitted to you, or any of the other > manufacturer's on this? > -- > PARSLEY CONSULTING > Ken Wagoner, SET > 760.745.6181 voice > 760.745.0537 fax > [email protected] <mailto:[email protected]> e-mail > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website > > > > Sal Izzo (TECH- 103) wrote: >> Reliable makes extended escutcheon plates (OOPS plateY for that purpose >> that fit over both friction fit escutcheons and cover plates for our >> sprinklers. These escutcheons are for aesthetic purposed only and do notr >> have to be part of any listed escutcheon assembly. Check the product >> solutions section of our website to see if the inner dimension will fit the >> sprinkler escutcheon you are using. >> >> Regards, >> >> Salvatore Izzo PE SFPE >> Mgr-Reliable Tech Services >> Sent from my Verizon Wireless BlackBerry >> >> -----Original Message----- >> From: Randy Knutson <[email protected]> >> Date: Fri, 19 Mar 2010 13:52:08 >> To: [email protected]<[email protected]> >> Subject: Over sized escutcheon for seismic clearances >> >> Forum Members, >> >> On one of our projects, we have to maintain a 2" clearance between the >> Armstrong ceiling tile and the sprinkler assembly. >> >> Do the escutcheon plates that cover this bigger hole have to be listed? We >> are using Tyco TY-FRB SSP's with recessed escutcheons and I don't see that >> Tyco manufactures an expansion plate. >> >> >> >> Any help would be appreciated. >> >> >> >> Randy Knutson, CET >> >> Sales Manager >> >> Shilo Automatic Sprinkler, Inc. >> >> 208-466-0006 ext 119 >> >> 208-466-7890 fax >> >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email to:[email protected] >> (Put the word unsubscribe in the subject field) >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email to:[email protected] >> (Put the word unsubscribe in the subject field) >> >> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)