Sal,

I wonder if a listing is required for the escutcheon Randy is referring 
to is required, since it is to be provided for something other than 
aesthetics, such as providing protection for the sprinkler head through 
a ceiling.  The provision for clearance is coming from a section of 
ASCE7.  I don't know if testing is required to confirm that the 
requisite clearance is provided or how the clearance from such an 
escutcheon would function in a seismic event.

Has there been any information transmitted to you, or any of the other 
manufacturer's on this?
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



Sal Izzo (TECH- 103) wrote:
> Reliable makes extended escutcheon plates (OOPS plateY  for that purpose that 
> fit over both friction fit escutcheons and cover plates for our sprinklers.  
> These escutcheons are for aesthetic purposed only and do notr have to be part 
> of any listed escutcheon assembly.  Check the product solutions section of 
> our website to see if the inner dimension will fit the sprinkler escutcheon 
> you are using.
>
> Regards,
>
> Salvatore Izzo PE SFPE
> Mgr-Reliable Tech Services
> Sent from my Verizon Wireless BlackBerry
>
> -----Original Message-----
> From: Randy Knutson <[email protected]>
> Date: Fri, 19 Mar 2010 13:52:08 
> To: [email protected]<[email protected]>
> Subject: Over sized escutcheon for seismic clearances
>
> Forum Members,
>
> On one of our projects, we have to maintain a 2" clearance between the
> Armstrong ceiling tile and the sprinkler assembly.
>
> Do the escutcheon plates that cover this bigger hole have to be listed? We
> are using Tyco TY-FRB SSP's with recessed escutcheons and I don't see that
> Tyco manufactures an expansion plate.
>
>  
>
> Any help would be appreciated.
>
>  
>
> Randy Knutson, CET
>
> Sales Manager
>
> Shilo Automatic Sprinkler, Inc.
>
> 208-466-0006 ext 119
>
> 208-466-7890 fax
>
>  
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to