ESFR sprinklers have a minimum area of coverage, so it's 12 sprinklers within the min/max range that they are listed to protect.
Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Friday, March 26, 2010 11:48 AM To: [email protected] Subject: ESFR for over 25ft storage NFPA 13 (07ed) section 16.3.3.4 requires a demand area of 12 ESFR sprinklers but it does not mention the 960sf minimum as in 22.4.4.3. Does this mean the minimum SF doesn't apply here? Thanks, Dewayne Martinez Design Build Fire Protection New Berlin, WI _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4946 (20100315) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 4946 (20100315) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)