Here is one that relies on an interpretation of the code from its literal
verbiage. NFPA 13: 8.15.19.5 states "When hydraulically designed systems
are revamped,
any existing bushing shall be removed and a nipple not exceeding 4 in. (100
mm) in length shall be permitted to be installed in the branch line
fitting."  This has historically been taken to mean that a 4 inch by 1/2
inch nipple can be installed in an existing 1 X ! X 1/2 tee to provide an
armover for a pendent sprinkler to a ceiling below.

However, this is not what the code states.  NFPA 13 is relating to a
bushing that was installed in an unfinished space.  In fact, it does not
state what size nipple is acceptable except that it cannot be less than 1
inch if it is in an earthquake zone.  As I read it, you cannot just remove
an upright sprinkler and install a 1/2 inch nipple connected to a 1/2 to 1
inch increaser and drop it to the ceiling below.  What is the consensus
and/or did the standard change sometime ago?

Thank You

Rahe Loftin, P.E.