Hey Guy's, really this is an approved method for upgrading an existing
system, wherein SSU were to be replaced with SSP heads, however as  it
invariably goes, a space is rented, ceiling goes up and overhead system
needs to be converted; gotta calc it, ref nodes at each change in pipe
size.............as to Seismic Zones, I believe it does not pertain, sorry
Ron; but if it is proven by hydraulic calculations (existing system upgrade
talkin here) then I believe the above situation is within code.

Thomas Poisal, CET


On Fri, Mar 26, 2010 at 8:25 PM, <[email protected]> wrote:

> Here is one that relies on an interpretation of the code from its literal
> verbiage. NFPA 13: 8.15.19.5 states "When hydraulically designed systems
> are revamped,
> any existing bushing shall be removed and a nipple not exceeding 4 in. (100
> mm) in length shall be permitted to be installed in the branch line
> fitting."  This has historically been taken to mean that a 4 inch by 1/2
> inch nipple can be installed in an existing 1 X ! X 1/2 tee to provide an
> armover for a pendent sprinkler to a ceiling below.
>
> However, this is not what the code states.  NFPA 13 is relating to a
> bushing that was installed in an unfinished space.  In fact, it does not
> state what size nipple is acceptable except that it cannot be less than 1
> inch if it is in an earthquake zone.  As I read it, you cannot just remove
> an upright sprinkler and install a 1/2 inch nipple connected to a 1/2 to 1
> inch increaser and drop it to the ceiling below.  What is the consensus
> and/or did the standard change sometime ago?
>
> Thank You
>
> Rahe Loftin, P.E.
> Region 7 - GSA
> Office - 817-978-7299
> Fax - 817-978-8644
> Cell - 817-371-3102
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to