The nipple as I remember had to be Sch 80 and I thought it was a close or space 
nipple max.

Sent on the Sprint® Now Network from my BlackBerry®

-----Original Message-----
From: Ron Greenman <[email protected]>
Date: Fri, 26 Mar 2010 18:39:15 
To: <[email protected]>
Subject: Re: 1/2 inch nipple in sprinkler outlet

Rahe,

I don't have my archival copies of 13 handy but I believe your
statement is only half right. Your reference is correct for your
second paragraph. The allowance for the 1/2 nipple not to exceed 4" in
length is elsewhere and used to have a drawing showing the arrangement
of a 1/2" Tee outlet with a 1/2" nipple transitioning to a 1/2" x 1"
Ell, a 1" short nipple, 1" Ell and finally the drop. This arrangement
has never been acceptable in a Seismic Zone.

On Fri, Mar 26, 2010 at 5:25 PM,  <[email protected]> wrote:
> Here is one that relies on an interpretation of the code from its literal
> verbiage. NFPA 13: 8.15.19.5 states "When hydraulically designed systems
> are revamped,
> any existing bushing shall be removed and a nipple not exceeding 4 in. (100
> mm) in length shall be permitted to be installed in the branch line
> fitting."  This has historically been taken to mean that a 4 inch by 1/2
> inch nipple can be installed in an existing 1 X ! X 1/2 tee to provide an
> armover for a pendent sprinkler to a ceiling below.
>
> However, this is not what the code states.  NFPA 13 is relating to a
> bushing that was installed in an unfinished space.  In fact, it does not
> state what size nipple is acceptable except that it cannot be less than 1
> inch if it is in an earthquake zone.  As I read it, you cannot just remove
> an upright sprinkler and install a 1/2 inch nipple connected to a 1/2 to 1
> inch increaser and drop it to the ceiling below.  What is the consensus
> and/or did the standard change sometime ago?
>
> Thank You
>
> Rahe Loftin, P.E.
> Region 7 - GSA
> Office - 817-978-7299
> Fax - 817-978-8644
> Cell - 817-371-3102
>
>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to