The 960 SF no longer is required (as of the 2010 edition anyways).  It
was intentionally deleted.  FM has never required a minimum size other
than whatever is provided by 12 sprinklers at their associated area of
coverage.  See ROP 13-456.

Roland

On Mar 26, 2010, at 1:20 PM, Dewayne Martinez wrote:

> 2007 also has 64sf.  I read a article by Kenneth Isman about ESFR 
> sprinklers and concrete tees which he staggers the sprinklers to meet 
> 8ft min between sprinklers.  He states that 960 SF still applies but 
> then I saw the section in Ch16 and was trying to confirm.  I have the 
> question into NFPA also.
> Dewayne
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> ParsleyConsulting
> Sent: Friday, March 26, 2010 2:44 PM
> To: [email protected]
> Subject: Re: ESFR for over 25ft storage
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to