George,

The obstruction has to be over 4'-0" wide in both directions.  Think about
it.  What if this light fixture was 8'-0" long by 0'-4" wide, would you put
sprinkler protection under that?

Benjamin Young
Sprinkler Designer
Rowe Sprinkler Systems, Inc.
[email protected]



On Mon, Mar 29, 2010 at 3:12 PM, George Medina Jr <[email protected]> wrote:

> I have a situation where I have an open ceiling tiled hallway and there are
> 2' x 4' light fixtures. According to NFPA-13 (2007) Sec. 8.6.5.3.3 it seems
> I need Coverage under a 4' wide fixed obstruction. My sprinklers are 5'
> above the lights. Do they need to have ceiling tiles in place around it or
> is there a solution I am missing. Any help would be greatly appreciated.
>
>
> George Medina Jr.