George, Maybe I'm missing something but the lights are only 2' wide and are not an obstruction based on the section you have mentioned below. I don't think you have any issue here.
Cliff Whitfield, SET President Fire Design, Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Medina Jr Sent: Monday, March 29, 2010 2:13 PM To: [email protected] Subject: 2'x4' Light Obstruction I have a situation where I have an open ceiling tiled hallway and there are 2' x 4' light fixtures. According to NFPA-13 (2007) Sec. 8.6.5.3.3 it seems I need Coverage under a 4' wide fixed obstruction. My sprinklers are 5' above the lights. Do they need to have ceiling tiles in place around it or is there a solution I am missing. Any help would be greatly appreciated. George Medina Jr. 323-236-1640 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)