George,

Maybe I'm missing something but the lights are only 2' wide and are not an
obstruction based on the section you have mentioned below.  I don't think
you have any issue here.

Cliff Whitfield, SET
President
Fire Design, Inc.



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Medina
Jr
Sent: Monday, March 29, 2010 2:13 PM
To: [email protected]
Subject: 2'x4' Light Obstruction

I have a situation where I have an open ceiling tiled hallway and there are
2' x 4' light fixtures. According to NFPA-13 (2007) Sec. 8.6.5.3.3 it seems
I need Coverage under a 4' wide fixed obstruction. My sprinklers are 5'
above the lights. Do they need to have ceiling tiles in place around it or
is there a solution I am missing. Any help would be greatly appreciated.


George Medina Jr. 