George, I have found it easier to say the "least" dimension has to be wider than 4ft. No coverage would be required below the lights in this case. Dewayne Martinez Design Build Fire Protection New Berlin, WI
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Medina Jr Sent: Monday, March 29, 2010 2:13 PM To: [email protected] Subject: 2'x4' Light Obstruction I have a situation where I have an open ceiling tiled hallway and there are 2' x 4' light fixtures. According to NFPA-13 (2007) Sec. 8.6.5.3.3 it seems I need Coverage under a 4' wide fixed obstruction. My sprinklers are 5' above the lights. Do they need to have ceiling tiles in place around it or is there a solution I am missing. Any help would be greatly appreciated. George Medina Jr. 323-236-1640 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)