George,
I have found it easier to say the "least" dimension has to be wider than
4ft.  
No coverage would be required below the lights in this case.
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Medina Jr
Sent: Monday, March 29, 2010 2:13 PM
To: [email protected]
Subject: 2'x4' Light Obstruction

I have a situation where I have an open ceiling tiled hallway and there
are 2' x 4' light fixtures. According to NFPA-13 (2007) Sec. 8.6.5.3.3
it seems I need Coverage under a 4' wide fixed obstruction. My
sprinklers are 5' above the lights. Do they need to have ceiling tiles
in place around it or is there a solution I am missing. Any help would
be greatly appreciated.


George Medina Jr. 