A 2' x 4' light fixture is only 2' wide, so there is no need for protection beneath. Although one dimension is 4', it is not 4' in its least dimension (width). Consider that there are probably conduits, pipes, and even the grid for the ceiling that are over 4' long, but you do not sprinkler below them for the same reason (the are under 4' wide).
Paul Pinigis, P.E. Life Safety Department Head -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Medina Jr Sent: Monday, March 29, 2010 3:13 PM To: [email protected] Subject: 2'x4' Light Obstruction I have a situation where I have an open ceiling tiled hallway and there are 2' x 4' light fixtures. According to NFPA-13 (2007) Sec. 8.6.5.3.3 it seems I need Coverage under a 4' wide fixed obstruction. My sprinklers are 5' above the lights. Do they need to have ceiling tiles in place around it or is there a solution I am missing. Any help would be greatly appreciated. George Medina Jr. 323-236-1640 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)