A 2' x 4' light fixture is only 2' wide, so there is no need for
protection beneath.  Although one dimension is 4', it is not 4' in its
least dimension (width).  Consider that there are probably conduits,
pipes, and even the grid for the ceiling that are over 4' long, but you
do not sprinkler below them for the same reason (the are under 4' wide).

Paul Pinigis, P.E.
Life Safety Department Head




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Medina Jr
Sent: Monday, March 29, 2010 3:13 PM
To: [email protected]
Subject: 2'x4' Light Obstruction

I have a situation where I have an open ceiling tiled hallway and there
are 2' x 4' light fixtures. According to NFPA-13 (2007) Sec. 8.6.5.3.3
it seems I need Coverage under a 4' wide fixed obstruction. My
sprinklers are 5' above the lights. Do they need to have ceiling tiles
in place around it or is there a solution I am missing. Any help would
be greatly appreciated.


George Medina Jr. 
323-236-1640
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to