George,
The way I do this is to average the lengths between heads.  For example, you
have a branch line with 6 heads.  They are spaced 8', 12', 9', 11', 7', &
10' apart.  The average will be 9.5' applying the 1.2 rule (assuming 1500
sf) you will have 4.89 (round up to 5) heads per line. If you use the
greatest distance of 12' you end up with only 3.87 (round up to 4) heads per
line.  If you chose to use the least dimension of 7' you will end up with
6.63 (round up to 7) heads per line.  7 seems like to many and 4 looks like
not enough.  This is why I average the distance between heads in a case such
as yours.

Bob Knight, CET
1660 Hill Rd
Melba, Idaho 83641
(208) 318-3057
(208) 495-2057 fax
b...@firebyknight.com
www.firebyknight.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina
Jr
Sent: Tuesday, April 20, 2010 12:41 AM
To: SprinklerFORUM@firesprinkler.org
Subject: Calc Area


If I am calculating a tree type system using the area/design method, and
have several different lengths between sprinklers on a branch line. Would I
use the longest length to determine the amount of 
sprinklers on a branch line. I have always used an average (which I've
probably been wrong all these years).

1.2vdesign area
           S 
S= Distance between sprinklers on branch line
 


1.2vdesign area
           S 
S= Distance between sprinklers on branch line
 



George Medina Jr. 


No virus found in this outgoing message.
Checked by AVG - www.avg.com 
Version: 9.0.801 / Virus Database: 271.1.1/2820 - Release Date: 04/19/10
00:31:00

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to