I don't think this is about density at all

-----Original Message-----
From: A.P.Silva [mailto:silva...@shaw.ca] 
Sent: Tuesday, April 20, 2010 2:13 PM
To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com
Subject: RE: Calc Area

If I understand what you are saying, it may not be correct either. If you
use the density corresponding to 1500 SF, then you don't have to check the
length again. If you use the density for 1640 SF, then you are right.

Tony 

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad
Sent: April 20, 2010 1:02 PM
To: sprinklerforum@firesprinkler.org; b...@firebyknight.com
Subject: RE: Calc Area

Why average anything--the actual dimensions are right there-- the thing I am
stressing is if you end up with 1640 SF area USED, go back and make sure 49'
does not put you more than half way to ANOTHER head on the line-- the 1.2
rule is for area USED, not minimum required area. 

-----Original Message-----
From: A.P.Silva [mailto:silva...@shaw.ca]
Sent: Tuesday, April 20, 2010 1:51 PM
To: sprinklerforum@firesprinkler.org; b...@firebyknight.com
Subject: RE: Calc Area

The critical factor is the length of the design area. Not the number of
heads. For 1500 RA and 1.2 shape factor this is approx. 46.5 feet. So taking
your example, it will be 5 heads per line, whichever side is the most
remote. Your method will work, but maybe not always. Say substitute 6' for
7' in your example. If the most remote area is the 8' side, now it is 6
heads on the line. If you use your method and take 5 heads per line the
minimum length of the design area will not be correct. 

Tony  

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Knight
Sent: April 20, 2010 12:30 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Calc Area

George,
The way I do this is to average the lengths between heads.  For example, you
have a branch line with 6 heads.  They are spaced 8', 12', 9', 11', 7', &
10' apart.  The average will be 9.5' applying the 1.2 rule (assuming 1500
sf) you will have 4.89 (round up to 5) heads per line. If you use the
greatest distance of 12' you end up with only 3.87 (round up to 4) heads per
line.  If you chose to use the least dimension of 7' you will end up with
6.63 (round up to 7) heads per line.  7 seems like to many and 4 looks like
not enough.  This is why I average the distance between heads in a case such
as yours.

Bob Knight, CET
1660 Hill Rd
Melba, Idaho 83641
(208) 318-3057
(208) 495-2057 fax
b...@firebyknight.com
www.firebyknight.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina
Jr
Sent: Tuesday, April 20, 2010 12:41 AM
To: SprinklerFORUM@firesprinkler.org
Subject: Calc Area


If I am calculating a tree type system using the area/design method, and
have several different lengths between sprinklers on a branch line. Would I
use the longest length to determine the amount of sprinklers on a branch
line. I have always used an average (which I've probably been wrong all
these years).

1.2vdesign area
           S
S= Distance between sprinklers on branch line
 


1.2vdesign area
           S
S= Distance between sprinklers on branch line
 



George Medina Jr. 


No virus found in this outgoing message.
Checked by AVG - www.avg.com 
Version: 9.0.801 / Virus Database: 271.1.1/2820 - Release Date: 04/19/10
00:31:00

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to