Thanks Cecil, Todd, and everybody else-- (please allow me this one time
Roland): When I am told "Brad, your job is not rocket science", I say "I
know, if it was it would not be so complicated. My job is to generate
billings based on delivery to a job site, in a Timely manner, an Approved
system of piping and components, Complete, and, it Fits. Do that with
Newton's Third Law!" :)
And Cecil you would have only one class to offer

-----Original Message-----
From: Todd Williams [mailto:t...@fpdc.com] 
Sent: Wednesday, April 21, 2010 8:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Calc Area

It is nice to know that I am not the only one that over-thinks 
things. I know Roland likes the world's fastest tractors, but you do 
have to beware the VW lest they become a Toyota (and this from a G1 
Prius owner).

T



At 09:05 PM 4/21/2010, you wrote:

>Brad and everybody else....
>
>
>
>OK.....  I'll bite.  It is amazing what can happen when you are busy 
>for a few days....
>
>
>
>First.  I know Roland is trying hard to be a nice guy (and not jump 
>all over you guys).... but... what the hell are you thinking?!?!?!
>
>
>
>Bob's dead, so I know this thread won't actually kill him.....
>
>
>
>USE the remote area size that you select from the density/area 
>curves to determine the length of the remote area.  No adjustment 
>necessary.  Unless of course I am competing with you.... then YOU... 
>MUST use the remote area that you actually put down on paper.....
>
>
>
>STOP IT!!  The length of the remote area must be at least as long as 
>this number:
>
>
>
>1.2 x sq rt A
>
>
>
>That's it!
>
>
>
>A: is the remote area you choose from the area desity curves.  Draw 
>a polyline that is exactly that long from the far corner of the 
>building (if this is how your building is so arranged) and if you 
>pass the midpoint of two sprinklers, then go to the next.  If you 
>are short of the midpoint...it's all good!
>
>
>
>These days, you CANNOT divide by spacing, because we don't use a 
>"spacing" for all of the sprinklers in a typical remote area.  As 
>Roland said, that's a CASUAL way to figure out if you are close....
>
>
>
>Next..... or second, adjust C-Factors?!?!?!?!?  STOP IT!!!!  If your 
>building has been around for more than 30 years, please.... feel 
>free.  C-Factors are based on 20 yr old pipe and they work fine for 
>nearly every building I have ever worked in.
>
>
>
>However, with a nod to the mad wizard (Scot), if an engineer 
>suspects anything and asks you to do it.... DO IT!!! And (with a nod 
>to the scalpel wielding KW) SHUT UP!!!!
>
>
>
>Brad, I think someone got in your head and said that this was a good 
>thing.  It is definitely more conservative and that is not a bad 
>thing.  Roland often speaks of Lamborghinis vs. Volkwagons.  If you 
>can afford to keep driving the Lamborghini, keep on keepin 
>on.  However, I am selling VW's and I am gonna sell way more cars 
>that way. And my customers will not only be happy..... they'll be alive!!!
>
>
>And finally, a nod to Professor Greenman and the incredible work he 
>does..... we are going to rock this industry as we change the way 
>people learn (Ron has some great ideas!!).  I hope that everyone 
>will soon hire designers that have a degree in Sprinkler System Technology.
>
>
>
>I'll figure out how to get George and other folks that are getting 
>old..... into another email sometime.... but we DO start a new 
>online Hydraulics Class soon (New Jersey Chapter is getting a 10% 
>discount on tuition).....
>
>
>
>Thanks to Steve Muncy and his cru that allow me to keep poppin' in....
>
>
>
>It should be recognized that the above is my opinion as a member of 
>the NFPA 13 Committee on Installation Criteria, and has not been 
>processed as a formal interpretation in accordance with the NFPA 
>Regulations Governing Committee Projects and should therefore not be 
>considered, nor relied upon, as the official position of the NFPA, 
>nor any of their technical committees.
>
>Sincerely,
>
>
>Cecil Bilbo
>Academy of Fire Sprinkler Technology
>Champaign, IL
>
>217-363-2460
>www.sprinkleracademy.com
>
>
>
>
> > From: bcasterl...@fsc-inc.com
> > To: sprinklerforum@firesprinkler.org
> > Subject: RE: Calc Area
> > Date: Tue, 20 Apr 2010 16:22:32 -0500
> >
> > So, Cecil, should I feel bad about leaving a box or 2 of heads off
remote
> > lines or not?
> >
> > -----Original Message-----
> > From: George Church [mailto:for...@ptd.net]
> > Sent: Tuesday, April 20, 2010 4:12 PM
> > To: sprinklerforum@firesprinkler.org
> > Subject: RE: Calc Area
> >
> > Y'all REALLY REALLY need to sign up for one of Cecil's online classes if
we
> > spend this much time talking about how we lay out the MRA. If 
> you're unsure,
> > or the code changed and you didn't, maybe it's time to go back to 
> school. No
> > shame in making sure you do it correctly from this crowd!
> >
> > And ya know the inspector and plan reviewer aren't gonna catch these
things
> > 98% of the time. So you'll either "get away" with a mistake, or you'll
be
> > defending your methodology in court, with your design guru(s) 
> sitting beside
> > you, facing the best forensic engineering talent money can buy.
Remember,
> > they may be looking to pin a couple to several million dollar loss on
YOU
> > and your insurance carrier. And if you carry $2m in coverage, have a $3m
> > loss, guess what happens to your house, business, car, etc? If you've
still
> > got assets to protect, I'd be careful to do it correctly. That MINIMUM
> > consensus standard isn't the end all, be all. It's a MINIMUM standard.
> >
> > glc
> >
> > -----Original Message-----
> > From: sprinklerforum-boun...@firesprinkler.org
> > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad
> > Sent: Tuesday, April 20, 2010 3:44 PM
> > To: sprinklerforum@firesprinkler.org
> > Subject: RE: Calc Area
> >
> > I was shocked when first confronted with the idea 8 years ago--- let us
see
> > what others have to say...
> >
> > -----Original Message-----
> > From: ParsleyConsulting [mailto:parsleyconsult...@cox.net]
> > Sent: Tuesday, April 20, 2010 2:35 PM
> > To: sprinklerforum@firesprinkler.org
> > Subject: Re: Calc Area
> >
> > Brad,
> >
> > I was intrigued by your remarks about having to re-evaluate the minimum
> > length of the remote area parallel to the branch lines if you were to
> > end up with a remote area of a different size than where the standard
> > initially had you start.
> >
> > I can't find anything in my copy of the NFPA-13 handbook, or the
> > Hydaulic Design text book by Pat Brock from Oklahoma State which even
> > remotely suggests this is a requirement.
> >
> > I've never done this, and I want to be sure I haven't missed something
> > critical. I need to be sure I understand what you're saying, because
> > for me the implications are huge for the plans I review on a daily basis
> > for a number of AHJ's.
> >
> > Are you stating that if in order to meet the requirements for a 1,500
> > square foot remote area I were to end up with a remote area of 1,600
> > square feet I then have to make an evaluation to make sure that the
> > length of the remote area parallel to the branch lines is at least 1.2 x
> > sqrt of 1,600? In effect, I need at least 48'-0", not the 46'-5" I
> > started with? If that's your position, can you give me some idea of how
> > you determined that such an additional requirement is necessary?
> >
> > I've got to tell you that if that is truly the case, I'm in seriously
> > deep trouble, as I've been doing calculations and plan reviews based on
> > a flawed premise, and that makes me really nervous.
> >
> > Can you give me/us some background on how you came to that conclusion?
> >
> > I'd really appreciate the help.
> > --
> >
> > PARSLEY CONSULTING
> >
> > Ken Wagoner, SET
> >
> > 760.745.6181 voice
> >
> > 760.745.0537 fax
> >
> > parsleyconsult...@cox.net <mailto:parsleyconsult...@cox.net> e-mail
> >
> > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
> >
> >
> > Brad wrote:
> > > I don't think this is about density at all
> > >
> > >
> > > -----Original Message-----
> > > From: A.P.Silva [mailto:silva...@shaw.ca]
> > > Sent: Tuesday, April 20, 2010 2:13 PM
> > > To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com
> > > Subject: RE: Calc Area
> > >
> > > If I understand what you are saying, it may not be correct either. If
you
> > > use the density corresponding to 1500 SF, then you don't have 
> to check the
> > > length again. If you use the density for 1640 SF, then you are right.
> > >
> > > Tony
> > >
> > > -----Original Message-----
> > > From: sprinklerforum-boun...@firesprinkler.org
> > > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad
> > > Sent: April 20, 2010 1:02 PM
> > > To: sprinklerforum@firesprinkler.org; b...@firebyknight.com
> > > Subject: RE: Calc Area
> > >
> > > Why average anything--the actual dimensions are right there-- the
thing I
> > am
> > > stressing is if you end up with 1640 SF area USED, go back and make
sure
> > 49'
> > > does not put you more than half way to ANOTHER head on the line-- the
1.2
> > > rule is for area USED, not minimum required area.
> > >
> > > -----Original Message-----
> > > From: A.P.Silva [mailto:silva...@shaw.ca]
> > > Sent: Tuesday, April 20, 2010 1:51 PM
> > > To: sprinklerforum@firesprinkler.org; b...@firebyknight.com
> > > Subject: RE: Calc Area
> > >
> > > The critical factor is the length of the design area. Not the number
of
> > > heads. For 1500 RA and 1.2 shape factor this is approx. 46.5 feet. So
> > taking
> > > your example, it will be 5 heads per line, whichever side is the most
> > > remote. Your method will work, but maybe not always. Say 
> substitute 6' for
> > > 7' in your example. If the most remote area is the 8' side, now it is
6
> > > heads on the line. If you use your method and take 5 heads per line
the
> > > minimum length of the design area will not be correct.
> > >
> > > Tony
> > >
> > > -----Original Message-----
> > > From: sprinklerforum-boun...@firesprinkler.org
> > > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob
Knight
> > > Sent: April 20, 2010 12:30 PM
> > > To: sprinklerforum@firesprinkler.org
> > > Subject: RE: Calc Area
> > >
> > > George,
> > > The way I do this is to average the lengths between heads. For
example,
> > you
> > > have a branch line with 6 heads. They are spaced 8', 12', 9', 11', 7',
&
> > > 10' apart. The average will be 9.5' applying the 1.2 rule (assuming
1500
> > > sf) you will have 4.89 (round up to 5) heads per line. If you use the
> > > greatest distance of 12' you end up with only 3.87 (round up to 4)
heads
> > per
> > > line. If you chose to use the least dimension of 7' you will end up
with
> > > 6.63 (round up to 7) heads per line. 7 seems like to many and 4 looks
> > like
> > > not enough. This is why I average the distance between heads in a case
> > such
> > > as yours.
> > >
> > > Bob Knight, CET
> > > 1660 Hill Rd
> > > Melba, Idaho 83641
> > > (208) 318-3057
> > > (208) 495-2057 fax
> > > b...@firebyknight.com
> > > www.firebyknight.com
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: sprinklerforum-boun...@firesprinkler.org
> > > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George
> > Medina
> > > Jr
> > > Sent: Tuesday, April 20, 2010 12:41 AM
> > > To: SprinklerFORUM@firesprinkler.org
> > > Subject: Calc Area
> > >
> > >
> > > If I am calculating a tree type system using the area/design method,
and
> > > have several different lengths between sprinklers on a branch line.
Would
> > I
> > > use the longest length to determine the amount of sprinklers on a
branch
> > > line. I have always used an average (which I've probably been wrong
all
> > > these years).
> > >
> > > 1.2vdesign area
> > > S
> > > S= Distance between sprinklers on branch line
> > >
> > >
> > >
> > > 1.2vdesign area
> > > S
> > > S= Distance between sprinklers on branch line
> > >
> > >
> > >
> > >
> > > George Medina Jr.
> > >
> > >
> > > No virus found in this outgoing message.
> > > Checked by AVG - www.avg.com
> > > Version: 9.0.801 / Virus Database: 271.1.1/2820 - Release Date:
04/19/10
> > > 00:31:00
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > Sprinklerforum@firesprinkler.org
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > For Technical Assistance, send an email to: supp...@firesprinkler.org
> > >
> > > To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > Sprinklerforum@firesprinkler.org
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > For Technical Assistance, send an email to: supp...@firesprinkler.org
> > >
> > > To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > Sprinklerforum@firesprinkler.org
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > For Technical Assistance, send an email to: supp...@firesprinkler.org
> > >
> > > To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > Sprinklerforum@firesprinkler.org
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > For Technical Assistance, send an email to: supp...@firesprinkler.org
> > >
> > > To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
> > > (Put the word unsubscribe in the subject field)
> > >
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@firesprinkler.org
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: supp...@firesprinkler.org
> >
> > To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@firesprinkler.org
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: supp...@firesprinkler.org
> >
> > To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@firesprinkler.org
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: supp...@firesprinkler.org
> >
> > To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@firesprinkler.org
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: supp...@firesprinkler.org
> >
> > To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
> > (Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum@firesprinkler.org
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: supp...@firesprinkler.org
>
>To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to