You could follow either (NFPA 13 - 2010) 8.5.7 for a skylight or deep pocket 
condition or 8.6.7 which permits a larger, but maximum 36 inch deep pocket.

Robert J. Pielow, P.E.
Fire Protection & Life Safety



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richardson, R
Sent: Thursday, April 22, 2010 10:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: skylights vs. ceiling pockets

When you say the "prescribed limitations on size and dimension" you must be 
referring to the ceiling pocket language.  

The problem is that the ceiling pocket section says you do not need to 
sprinkler skylights separated by 10 ft. each one less than 32 sq.ft. with no 
apparent restrictions on depth.

Rich

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Pielow, Robert
Sent: Thursday, April 22, 2010 08:53
To: sprinklerforum@firesprinkler.org
Subject: RE: skylights vs. ceiling pockets

I do not believe NFPA 13 requires a sprinkler in either a pocket or skylight 
that meet the prescribed limitations on size and dimension.  The recesses are 
required to be separated by at least 10 feet so any delay caused by the height 
of the pocket would not have an impact.  The sprinkler handbook provides a good 
description of this condition.  It references skylights or "similar pockets".

Robert J. Pielow, P.E.


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richardson, R
Sent: Thursday, April 22, 2010 10:38 AM
To: sprinklerforum@firesprinkler.org
Subject: skylights vs. ceiling pockets

Am I understanding the standard correctly in that a ceiling pocket that would 
otherwise require sprinklers may no longer require sprinklers if I were to 
install a skylight in the pocket, regardless of depth etc.?  

If the answer is yes, any logical reasons one could offer would be helpful. 

Thanks,

Rich Richardson
Seattle Fire Department
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to