Unless explicitly allowed, such as QR in mechanical closet, you can  
NOT mixing different types of sprinklers in one compartment.  What  
would be your method for combining the different design basis for each  
type of sprinkler?

Roland

On Apr 26, 2010, at 9:40 PM, A.P.Silva wrote:

> Reviewing a drawing where the designer has both residential and quick
> response heads in a dwelling unit. A res head is installed where the
> coverage is required to be EC. In other areas non-residential QR  
> sprinklers.
> First, I don't think there's a problem mixing heads. Is that correct?
> Second, can room design method be used, provided minimum 4 heads are  
> calcd.?
>
> Tony
>