Or using a higher-temp sprinkler in an area that's influenced by a heat
source.  We sometimes mix a 200 QR spray sprinkler into a residential
compartment when there's a fireplace of cooking appliance to consider.

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Tuesday, April 27, 2010 1:18 PM
To: [email protected]
Subject: Re: Mixing residential/qr heads

Unless explicitly allowed, such as QR in mechanical closet, you can  
NOT mixing different types of sprinklers in one compartment.  What  
would be your method for combining the different design basis for each  
type of sprinkler?

Roland

On Apr 26, 2010, at 9:40 PM, A.P.Silva wrote:

> Reviewing a drawing where the designer has both residential and quick
> response heads in a dwelling unit. A res head is installed where the
> coverage is required to be EC. In other areas non-residential QR  
> sprinklers.
> First, I don't think there's a problem mixing heads. Is that correct?
> Second, can room design method be used, provided minimum 4 heads are  
> calcd.?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4946 (20100315) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to