I am trying to find out how a new rule is added into 13 without having a
bar next to it in the margin and without being in the ROP or the ROC?

Case in point. NFPA 13, 2007 Section 18.2.4. "The protection specified
in 18.2.1 shall not be required where ESFR or large drop sprinkler
systems that are approved for rubber tire storage are installed." There
is no bar in the margin yet column sprinklers are required in rubber
tire storage in the 02 edition, see Section 12.4.1.

We have an AHJ that won't let us use any part of the 07 edition on a
rubber tire storage project because it has not been adopted by the city.
I thought I would submit that 1.6 allows new technologies and the
currently available ESFR's do not require column protection. I am trying
to find where the language in 18.2.4 (07) came from to use as back up.

Ron Fletcher
Aero Automatic
Phoenix, AZ  