There is no prohibition to having a pre-action system adjacent to a wet sprinkler system. There might be storage configurations or processes where you want the additional protection of a double interlocked pre-action system, but there is no need for that level through the remaining spaces. The detection would only be required over the area protected by the pre action system.
Robert J. Pielow, P.E. Fire Protection & Life Safety -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Richardson, R Sent: Thursday, May 06, 2010 12:27 PM To: [email protected] Subject: Pre-action in same space as wet pipe system Seeking opinions about a proposal where a pre-action system covers part of a large space, the other parts being covered with a wet pipe system. There is no separation between the two system types. Thanks in advance, Rich Richardson Seattle Fire Department _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)