In any installation recessed light fixtures typically pose no issue in respect 
to sprinkler locations.  

If you're talking about pendent style fixtures, the location in respect to the 
sprinkler becomes an obstruction issue and has plenty of NFPA reference 
material for requiring relocation of the sprinkler or light.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Eric Tysinger
Sent: Tuesday, May 11, 2010 1:48 PM
To: [email protected]
Subject: RE: 

I completely agree, but why aren't the non-fluorescent lights addressed for 
non-residential areas? When we tell a customer the sprinkler needs to be moved 
away from the light and they ask for a code reference what do you tell them? In 
this market you can't always sell preferences or looks. When we know it 
shouldn't be right next to it.

Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, May 11, 2010 1:33 PM
To: [email protected]
Subject: RE: 

Fluorescent light fixtures and HVAC diffusers should not be confused as far as 
heat output.  

Typically as said before in a 2x2 grid ceiling the Architect likes to see heads 
in centers of tiles.  If you do not have that restriction then do whatever 
works but realize that a consistent spacing from the edge of the grid makes for 
a better looking / less offensive appearing system from the A/E and owner 
perspective.  Noting that in odd shaped rooms it can often be a challenge to 
make the system work AND make people happy.  But there's nothing more 
aggravating to the architect than some random shotgun approach to head spacing. 
 

Usually I try to stay no less than 6" off the grid whenever possible if I have 
no Center-of-tile mandate.  But the fluorescent fixture poses no heat issue in 
regards to the sprinkler.  Now an incandescent fixture, MV, MH or Halogen, 
different story.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Eric Tysinger
Sent: Tuesday, May 11, 2010 1:23 PM
To: [email protected]
Subject: RE: 

Look at the requirement for 155F sprinklers in relation to hot air diffusers.

8.3.2.5 (c) - Residential areas require 24" for ceiling mounted diffusers.

8.3.2.5 (a) - Non-Residential areas require 12" for ceiling mounted diffusers.

Why the difference? Actually 8.3.2.5(c) reads "residential areas" not 
residential sprinklers.

Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Richard Carr
Sent: Tuesday, May 11, 2010 1:08 PM
To: [email protected]
Subject: RE: 

Yes it does but with no other guidelines to go by I always used it as a minimum 
to keep the heads away, figuring the Residential heads and QR heads have 
different spray patterns but should still react the same to a heat from a light 
fixture.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[email protected]




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eric Tysinger
Sent: Tuesday, May 11, 2010 12:52 PM
To: [email protected]
Subject: RE: 

8.3.2.5(c) is for residential sprinklers. Worth indicates light hazard/quick 
response.

8.3.2.5(A)(B) do not have any requirements in regards to light fixtures.

All based on 2007 edition. 2002 is the same.

Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard Carr
Sent: Tuesday, May 11, 2010 12:22 PM
To: [email protected]
Subject: RE: 

Table 8.3.2.5(c) will give you the distance from light based on head temp.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Anderson, Worth
Sent: Tuesday, May 11, 2010 12:19 PM
To: [email protected]; [email protected]
Subject: RE: 

Heat Source refers to preaction and deluge systems, 7.3.1.8.2.3?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, May 11, 2010 12:11 PM
To: [email protected]
Subject: Re:

You need to look at distance from heat sources, not obstructions.
Mark Eckard
[email protected]

-----Original Message-----
From: "Anderson, Worth" <[email protected]>
Date: Tue, 11 May 2010 11:52:37
To: <[email protected]>
Subject: RE: 

Light fixture is flush with ceiling grid. Just having some difficulty locating 
minimum distance in NFPA 13 2007. 

Worth Anderson
Cintas Fire Protection
E-mail: [email protected]
Phone: (239)-693-8722 Ext: 224
   Cell:  (239)-633-3887
   Fax   (239)-693-8792
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cliff Whitfield
Sent: Tuesday, May 11, 2010 11:48 AM
To: [email protected]
Subject: RE: 

How far does the light stick down from the ceiling and how far is your 
sprinkler deflector from the ceiling?

Cliff
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Anderson, Worth
Sent: Tuesday, May 11, 2010 10:42 AM
To: [email protected]
Subject: 

What is the minimum deflection distance of a pendant sprinkler head from
(2'x4') florescent light
fixture with (2'x2') ceiling tile throughout? Area of work is Light Hazard / 
Quick Response pendant heads. 

 

Thanks,  

 

 


This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.
Your assistance in correcting this error is appreciated.  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.
Your assistance in correcting this error is appreciated.  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.
Your assistance in correcting this error is appreciated.  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


This email and any attached files are confidential and intended solely for the 
intended recipient(s). If you are not the named recipient you should not read, 
distribute, copy or alter this email. Any views or opinions expressed in this 
email are those of the author and do not represent those of the  company. 
Warning: Although precautions have been taken to make sure no viruses are 
present in this email, the company cannot accept responsibility for any loss or 
damage that arise from the use of this email or attachments.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


This email and any attached files are confidential and intended solely for the 
intended recipient(s). If you are not the named recipient you should not read, 
distribute, copy or alter this email. Any views or opinions expressed in this 
email are those of the author and do not represent those of the  company. 
Warning: Although precautions have been taken to make sure no viruses are 
present in this email, the company cannot accept responsibility for any loss or 
damage that arise from the use of this email or attachments.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
  • RE: Cliff Whitfield
  • Re: me
    • RE: Anderson, Worth
      • RE: Richard Carr
        • RE: Eric Tysinger
          • RE: Richard Carr
          • RE: Eric Tysinger
          • RE: Cliff Whitfield
          • RE: Craig.Prahl
          • RE: Eric Tysinger
          • RE: Craig.Prahl
          • RE: Anderson, Worth

Reply via email to