Since everything is remaining the same except the diameter of the last  
piece of pipe, the question you have to answer for your AHJ is - does  
the change increase or decrease the system demand when compared to the  
original calculation?  That will answer your question.

Roland

On May 11, 2010, at 1:31 PM, Charles Thurston wrote:

> Hello All you Fine folks of the Sprinklerforum,
>
> I am looking at replacing all the pipe in a 2 story parking deck   
> due to external corrosion (The fitters will love to be to look at  
> the beach while they "work"). 3" main fed from a 500 GMP ??PSI pump.  
> The building the pump feeds is 16 stories of  condos.
> Each branch line feeds 5 heads now.
> 1 1/4" from main feeds heads 1-4 and 1" to the 5th head. It will be  
> cheaper to run the branch line all the way out in 1 1/4 fitting and  
> machine adjustment wise. The AHJ "ask" if it was allowable to change  
> the pipe size without re-calcing the entire system. It is planned to  
> measure out the pipe lengths and out the heads back in the same  
> locations. I have not found anything in NFPA 13 2007 addressing  
> this. Does anybody know a reason not to run 1 1/4" all the way out  
> other than to "balance the flow" in the last head.
>
> -- 
> Best regards,
> Charles Thurston                          mailto:[email protected]
>  Coastal Fire Protection/ Myrtle Beach Fire & Safety Group.
>  AFAA Guest
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to