That's just it.  Some scenarios reduce the end head condition and the overall 
friction loss in the system.  Some scenarios increase the overdischarge and 
therefore the friction loss in the pipes.  Unless you AND the AHJ are well 
versed with hydraulics, you will end up doing calcs to prove the situation.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487


-----Original Message-----
From: Russell [mailto:[email protected]] 
Sent: Wednesday, May 12, 2010 1:25 PM
To: [email protected]
Subject: RE: Pipe Size

I give. 

Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Wednesday, May 12, 2010 12:47 PM
To: [email protected]
Subject: RE: Pipe Size

Actually K8.0 could be a very good choice for LH if you use 14x14 spacing.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Russell
Sent: Wednesday, May 12, 2010 10:19 AM
To: [email protected]
Subject: RE: Pipe Size

Well, what I'm getting at is that the more water that is flowing from the
remote area the less residual pressure you have available at the source. The
less residual, the less the safety factor. The same as trying to use
sprinklers with a k-factor of 8.0 in a light hazard design. It'll kill your
calc's.

Russell

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 9.0.819 / Virus Database: 271.1.1/2869 - Release Date: 05/12/10
02:26:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to