Mis-type, the increase in gallons is about 1.5, the reduced starting 
pressure is 5.25 psi.

Wrong keys, seems to be a theme for me this week.
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



ParsleyConsulting wrote:
> My first thought when I read this was "What?"
>
> Then I grabbed the calculator.  Sure enough, at 196 sqft spacing, 
> requiring 19.6 gpm....
>
> Using a 5.6 k-factor sprinkler the starting pressure is 12.25 psi, 
> roughly, giving you 19.6 gpm
>
> Using an 8.0 k-factor sprinkler the starting pressure has to be at least 
> 7.0 psi, giving you 21.16 gpm.
>
> Slightly higher flow, with about 1.5 psi reduced starting pressure.  
> Wonder how big an RA you have to get to before the increased flow starts 
> to take it's toll.
>
> Food for thought, Thom, and thanks!
>   