Hello George,

Yes there are.

Wednesday, May 12, 2010, 11:14:19 AM, you wrote:

> Aren't there like 15 or 20 stories above us in this one? 

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd Williams
> Sent: Wednesday, May 12, 2010 11:03 AM
> To: [email protected]
> Subject: Re: Pipe Size

> The caveat with that is if you have a very steep supply curve and the 
> system is designed tight to it, you may want to check that you have 
> enough volume.


> At 10:59 AM 5/12/2010, you wrote:
>>Without a doubt it will increase the total amount of water discharged
>>at available pressure but that is not a bad thing.  The larger pipe
>>will not only reduce the required pressure, it will also lower the
>>required Q by reducing excess discharge / overage.   If the system
>>demand is less then the surplus pressure is greater and once that is
>>shown to the AHJ, every one should be a happy camper.

>>Roland

>>On May 12, 2010, at 7:45 AM, Russell wrote:

>> > Increasing the pipe sizes upstream of the remote sprinkler can cause a
>> > situation called "over spray" or "excess discharge". This increased
>> > discharge increases the total water demand on the supply which in turn
>> > lowers the available pressure which will decrease the safety margin.
>> > Just
>> > from my experiences.
>> >
>> > Russell Rewis
>> > Brown Automatic Sprinklers, Inc.
>> > 107C Hemlock Street
>> > Valdosta, Georgia 31601
>> > 229-244-8130

>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

>>For Technical Assistance, send an email to: [email protected]

>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)

> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



-- 
Best regards,
Charles Thurston
Coastal Fire Protection
 Coastal                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to