I'd ask him to please, for your edification, cite the sections of the NFPA 
Standard where he derived his specification data.  

I guess he was looking at sprinkler data sheets and when it didn't say that the 
sprinkler is designed for 0.10 or whatever gpm/sq. ft he thinks it falls into 
that category?


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, May 19, 2010 6:11 AM
To: [email protected]
Subject: 13R sprinklers

I am working on a project with a rather ignorant engineer who will 
not accept listed flow requirements for residential sprinklers. He is 
insisting on using the 12 x 12 spacing, 13 gpm for multiple sprinkler 
flow and 18 for single sprinkler flow (we have to calculate both). My 
question may be one of semantics, but this is what the engineer is 
hanging everything on. Both the above spacing and discharge 
requirements are under sections entitled "Sprinklers That Have Not 
Been Listed with Specific (Discharge/Coverage) Criteria". Since 
virtually all of the residential sprinklers I am aware of have 
specific design and coverage criteria, am I to assume based on the 
wording that sprinklers with specific criteria cannot be used under 
this section? If so, are there any sprinklers without specific 
criteria currently on the market?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to