Todd ,
 Are you saying the engineer has seen and has read these sections of 13R and 
still doesn't understand the requirements ? If so , you may have to go over his 
head to a higher authority or say a prayer and try to appease him as best you 
can.

Good Luck ,

Lamar Vaughn , SET

  
---- Todd Williams <[email protected]> wrote: 
> Discharge - 6.7.1.1.1, Coverage - 6.7.1.3.1. NFPA 13R (2002)
> 
> 
> 
> At 08:23 AM 5/19/2010, you wrote:
> >I'd ask him to please, for your edification, cite the sections of 
> >the NFPA Standard where he derived his specification data.
> >
> >I guess he was looking at sprinkler data sheets and when it didn't 
> >say that the sprinkler is designed for 0.10 or whatever gpm/sq. ft 
> >he thinks it falls into that category?
> >
> >
> >Craig L. Prahl, CET
> >Fire Protection Specialist
> >Mechanical Department
> >CH2MHILL
> >Lockwood Greene
> >1500 International Drive
> >Spartanburg, SC  29304-0491
> >Direct - 864.599.4102
> >Fax - 864.599.8439
> >[email protected]
> >http://www.ch2m.com
> >
> >-----Original Message-----
> >From: [email protected] 
> >[mailto:[email protected]] On Behalf Of Todd Williams
> >Sent: Wednesday, May 19, 2010 6:11 AM
> >To: [email protected]
> >Subject: 13R sprinklers
> >
> >I am working on a project with a rather ignorant engineer who will
> >not accept listed flow requirements for residential sprinklers. He is
> >insisting on using the 12 x 12 spacing, 13 gpm for multiple sprinkler
> >flow and 18 for single sprinkler flow (we have to calculate both). My
> >question may be one of semantics, but this is what the engineer is
> >hanging everything on. Both the above spacing and discharge
> >requirements are under sections entitled "Sprinklers That Have Not
> >Been Listed with Specific (Discharge/Coverage) Criteria". Since
> >virtually all of the residential sprinklers I am aware of have
> >specific design and coverage criteria, am I to assume based on the
> >wording that sprinklers with specific criteria cannot be used under
> >this section? If so, are there any sprinklers without specific
> >criteria currently on the market?
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, CT
> >860.535.2080
> >www.fpdc.com
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to