This is important - LET ME PLAY DEVIL'S ADVOCATE, where is the engineer
WRONG?  Quick look at Tyco LF II 4.9 pendant 12' x 12' is 13 gpm.  And at 18
gpm it's a 13.49 psi start.  The sidewalls at 4.2 will do 13gpm at 9.2 psi
so you are not forced under a 7 psi start. So he won't let you use 16' x 20'
spacing?  Just because one won't allow what in essence is extended coverage
doesn't make one ignorant. 

Is this not the equivalent of not allowing sched 7 and only allowing sched
40 threaded noting sched 7 has many more times the CRR?  Both cases are text
book verse a real application.  Perhaps some think 12' x 12' spacing is
better then EC and 40 is better than 7 when applied to a real project.  How
often do we see a spec say no EC? How often do we see no reduction for QR?

I acknowledge you did say he is reading out of the where not been listed
with special...so his argument may be flawed but his conclusion probably
isn't from his perspective.  I'm sure you recall the 13/18 was the original
NFPA 13R/D spec and the first heads had no other spacing options.  But it
also looks like at least in Tyco's case the low end it's the same on the
13gpm side.  Yeah the dual gpm is gone.  But an engineer can spec any
density greater than the minimum.     

I didn't talk with the engineer perhaps he/she/it is ignorant or perhaps
just exercising engineering prerogative like all the other times we see it.


Again that was the other side of the coin.  I'M ON YOUR SIDE TODD.  I
wouldn't cost the owner extra money in what will probably be a lot of extra
heads but I don't see anything WRONG here. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, May 19, 2010 8:39 AM
To: [email protected]
Subject: RE: 13R sprinklers

Todd ,
 Are you saying the engineer has seen and has read these sections of 13R and
still doesn't understand the requirements ? If so , you may have to go over
his head to a higher authority or say a prayer and try to appease him as
best you can.

Good Luck ,

Lamar Vaughn , SET

  
---- Todd Williams <[email protected]> wrote: 
> Discharge - 6.7.1.1.1, Coverage - 6.7.1.3.1. NFPA 13R (2002)
> 
> 
> 
> At 08:23 AM 5/19/2010, you wrote:
> >I'd ask him to please, for your edification, cite the sections of 
> >the NFPA Standard where he derived his specification data.
> >
> >I guess he was looking at sprinkler data sheets and when it didn't 
> >say that the sprinkler is designed for 0.10 or whatever gpm/sq. ft 
> >he thinks it falls into that category?
> >
> >
> >Craig L. Prahl, CET
> >Fire Protection Specialist
> >Mechanical Department
> >CH2MHILL
> >Lockwood Greene
> >1500 International Drive
> >Spartanburg, SC  29304-0491
> >Direct - 864.599.4102
> >Fax - 864.599.8439
> >[email protected]
> >http://www.ch2m.com
> >
> >-----Original Message-----
> >From: [email protected] 
> >[mailto:[email protected]] On Behalf Of Todd
Williams
> >Sent: Wednesday, May 19, 2010 6:11 AM
> >To: [email protected]
> >Subject: 13R sprinklers
> >
> >I am working on a project with a rather ignorant engineer who will
> >not accept listed flow requirements for residential sprinklers. He is
> >insisting on using the 12 x 12 spacing, 13 gpm for multiple sprinkler
> >flow and 18 for single sprinkler flow (we have to calculate both). My
> >question may be one of semantics, but this is what the engineer is
> >hanging everything on. Both the above spacing and discharge
> >requirements are under sections entitled "Sprinklers That Have Not
> >Been Listed with Specific (Discharge/Coverage) Criteria". Since
> >virtually all of the residential sprinklers I am aware of have
> >specific design and coverage criteria, am I to assume based on the
> >wording that sprinklers with specific criteria cannot be used under
> >this section? If so, are there any sprinklers without specific
> >criteria currently on the market?
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, CT
> >860.535.2080
> >www.fpdc.com
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to