And I used to have a Pacer and loved it except for the heavy handling front end.

On Wed, May 19, 2010 at 8:10 AM, George Church <[email protected]> wrote:
> Todd, please refrain from making fun of engineers like that. I know one that
> just gave up his Saturn and dresses like a tourist. And I've seen worser,
> LOL.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd Williams
> Sent: Wednesday, May 19, 2010 10:52 AM
> To: [email protected]
> Subject: RE: 13R sprinklers
>
> I am going with ignorant. In addition to this, we have to sprinkler
> all closets and bathrooms, install an RPZ in a hot box outside the
> building and they took my 42x30 drawing, shrunk it to 36x24, then
> rejected the plan for being less than 1/8 scale.
>
> I remember the 13/18 was the original design, but the single head
> calc went out about 10 years ago(?). The spec also calls for Grinnell
> or Star sprinklers. My guess is the engineer is just not current and
> not interested in being so. He probably drives and AMC Hornet and
> wear a leisure suit.
>
>
>
> At 10:26 AM 5/19/2010, you wrote:
>>This is important - LET ME PLAY DEVIL'S ADVOCATE, where is the engineer
>>WRONG?  Quick look at Tyco LF II 4.9 pendant 12' x 12' is 13 gpm.  And at
> 18
>>gpm it's a 13.49 psi start.  The sidewalls at 4.2 will do 13gpm at 9.2 psi
>>so you are not forced under a 7 psi start. So he won't let you use 16' x
> 20'
>>spacing?  Just because one won't allow what in essence is extended coverage
>>doesn't make one ignorant.
>>
>>Is this not the equivalent of not allowing sched 7 and only allowing sched
>>40 threaded noting sched 7 has many more times the CRR?  Both cases are
> text
>>book verse a real application.  Perhaps some think 12' x 12' spacing is
>>better then EC and 40 is better than 7 when applied to a real project.  How
>>often do we see a spec say no EC? How often do we see no reduction for QR?
>>
>>I acknowledge you did say he is reading out of the where not been listed
>>with special...so his argument may be flawed but his conclusion probably
>>isn't from his perspective.  I'm sure you recall the 13/18 was the original
>>NFPA 13R/D spec and the first heads had no other spacing options.  But it
>>also looks like at least in Tyco's case the low end it's the same on the
>>13gpm side.  Yeah the dual gpm is gone.  But an engineer can spec any
>>density greater than the minimum.
>>
>>I didn't talk with the engineer perhaps he/she/it is ignorant or perhaps
>>just exercising engineering prerogative like all the other times we see it.
>>
>>
>>Again that was the other side of the coin.  I'M ON YOUR SIDE TODD.  I
>>wouldn't cost the owner extra money in what will probably be a lot of extra
>>heads but I don't see anything WRONG here.
>>
>>Chris Cahill, P.E.
>>Fire Protection Engineer
>>Sentry Fire Protection, Inc.
>>
>>763-658-4483
>>763-658-4921 fax
>>
>>Email: [email protected]
>>
>>Mail: P.O. Box 69
>>         Waverly, MN 55390
>>
>>Location: 4439 Hwy 12 SW
>>               Waverly, MN 55390
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of
>>[email protected]
>>Sent: Wednesday, May 19, 2010 8:39 AM
>>To: [email protected]
>>Subject: RE: 13R sprinklers
>>
>>Todd ,
>>  Are you saying the engineer has seen and has read these sections of 13R
> and
>>still doesn't understand the requirements ? If so , you may have to go over
>>his head to a higher authority or say a prayer and try to appease him as
>>best you can.
>>
>>Good Luck ,
>>
>>Lamar Vaughn , SET
>>
>>
>>---- Todd Williams <[email protected]> wrote:
>> > Discharge - 6.7.1.1.1, Coverage - 6.7.1.3.1. NFPA 13R (2002)
>> >
>> >
>> >
>> > At 08:23 AM 5/19/2010, you wrote:
>> > >I'd ask him to please, for your edification, cite the sections of
>> > >the NFPA Standard where he derived his specification data.
>> > >
>> > >I guess he was looking at sprinkler data sheets and when it didn't
>> > >say that the sprinkler is designed for 0.10 or whatever gpm/sq. ft
>> > >he thinks it falls into that category?
>> > >
>> > >
>> > >Craig L. Prahl, CET
>> > >Fire Protection Specialist
>> > >Mechanical Department
>> > >CH2MHILL
>> > >Lockwood Greene
>> > >1500 International Drive
>> > >Spartanburg, SC  29304-0491
>> > >Direct - 864.599.4102
>> > >Fax - 864.599.8439
>> > >[email protected]
>> > >http://www.ch2m.com
>> > >
>> > >-----Original Message-----
>> > >From: [email protected]
>> > >[mailto:[email protected]] On Behalf Of Todd
>>Williams
>> > >Sent: Wednesday, May 19, 2010 6:11 AM
>> > >To: [email protected]
>> > >Subject: 13R sprinklers
>> > >
>> > >I am working on a project with a rather ignorant engineer who will
>> > >not accept listed flow requirements for residential sprinklers. He is
>> > >insisting on using the 12 x 12 spacing, 13 gpm for multiple sprinkler
>> > >flow and 18 for single sprinkler flow (we have to calculate both). My
>> > >question may be one of semantics, but this is what the engineer is
>> > >hanging everything on. Both the above spacing and discharge
>> > >requirements are under sections entitled "Sprinklers That Have Not
>> > >Been Listed with Specific (Discharge/Coverage) Criteria". Since
>> > >virtually all of the residential sprinklers I am aware of have
>> > >specific design and coverage criteria, am I to assume based on the
>> > >wording that sprinklers with specific criteria cannot be used under
>> > >this section? If so, are there any sprinklers without specific
>> > >criteria currently on the market?
>> > >
>> > >Todd G. Williams, PE
>> > >Fire Protection Design/Consulting
>> > >Stonington, CT
>> > >860.535.2080
>> > >www.fpdc.com
>> > >
>> > >_______________________________________________
>> > >Sprinklerforum mailing list
>> > >[email protected]
>> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> > >
>> > >For Technical Assistance, send an email to: [email protected]
>> > >
>> > >To Unsubscribe, send an email
> to:[email protected]
>> > >(Put the word unsubscribe in the subject field)
>> > >_______________________________________________
>> > >Sprinklerforum mailing list
>> > >[email protected]
>> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> > >
>> > >For Technical Assistance, send an email to: [email protected]
>> > >
>> > >To Unsubscribe, send an email
> to:[email protected]
>> > >(Put the word unsubscribe in the subject field)
>> >
>> > Todd G. Williams, PE
>> > Fire Protection Design/Consulting
>> > Stonington, CT
>> > 860.535.2080
>> > www.fpdc.com
>> >
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > For Technical Assistance, send an email to: [email protected]
>> >
>> > To Unsubscribe, send an email
> to:[email protected]
>> > (Put the word unsubscribe in the subject field)
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to