Ok, I may have missed this in the discussion, but what did the plans and
spec. call for?
Design per 13R?
If this eng. Is as lame as it sounds he is most likely he's not an FPE. Just
a ME who "I've been doing this for years."
Well as I see it he can require greater than 0.05 GPM/SF or 12x12 spacing
only if he asked for it in the bid doc.'s, if not and he still wants it, he
can forward your C.O. to the owner, for making it that way.

As Ken said:
Increased meter size
Increased pipe size
Increased number of sprinkler heads
Delay of project
Increased burden, OH Profit Insurance Bond cost
Stacking of trades
Lost efficiency from delay
Increased supervision for increased crew size
Compressive acceleration of schedule

Pay a couple of hundred bucks and get an FPE registered in CT to write a
nice letter stating that what the EOR wants is in excess of what is required
by the codes or standards (and Spec. if that applies).


Now you're ready when he forwards your C.O. to the Arch. With a
recommendation to Deny it.