Read my last paragraph. I do agree with you in my professional opinion.  But
we are talking two different contexts on wrong when I was playing devil's
advocate.  The engineer is wrong on the moral wrong but not on the legal
aspect of wrong. You expounded on the moral wrong increasing costs, as I
said I agree.  It is morally incomprehensible to add tremendous costs
without articulate and accurate justification. On the legal issues the
engineer is not wrong. He can set any limits he wants as long as they are
not in violation of the MIMINUM law. If he wanted 6'x6' spacing max then
he'd be both morally and legally wrong when using res heads and no baffles. 

If you are going to argue with an engineer you need to understand the
difference between the two contexts of wrong to be able to attack
appropriately.  You can't win a moral argument with a legal challenge.  You
need to attack the morally incomprehensible added costs, which you have done
nicely. 

And quite frankly in this case he is closer to the average engineer work
product, IMHO.  And remember the forum engineers are all above average.
This moral/legal distinction is why so many engineers practice fire
protection without fear from a PE board. Most of the time they are legally
correct even if out on a limb with facts and science.  I can't actually
think of a case off the top of my head of first hand involvement of a legal
wrong.  I have a pile of differences of opinion.   

One good way to change the engineers mind is to bid as shown and offer an
alternate for what we'd call a common modern standard system.  Odds are the
engineer is not involved in the cost side of the matter.    

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
ParsleyConsulting
Sent: Wednesday, May 19, 2010 10:36 AM
To: [email protected]
Subject: Re: 13R sprinklers

Chris,

I'll can tell you exactly where the SOB-PE is wrong.  Consider a 16' x 
16' room.  How many residential sprinklers?

In the world of the listing criteria from Tyco, or any other 
manufacturer, this room requires a single sprinkler, absent anything 
that would prevent it not exceeding 10' from a wall.

In the world of the PE who Todd is dealing with, the answer is no, you 
must install four sprinklers, because your coverage cannot exceed 12' x 
12', or 6'-0" from any wall.  He has quadrupled the number of sprinklers 
in the room, and I might add, quadrupled the cost of the sprinkler 
system to the customer.  And this will hold true in every room in the 
building which is greater than 12'x12' in size. 

Here's another part of that consideration.  The same aforementioned 
16'x16' room, would require the hydraulic calculations to prove that 
13.0 gpm would be delivered to the single sprinkler in the room, if the 
listing criteria and NFPA-13D were followed.  In the world of the PE, 
that changes again, and now Todd has to prove that 26 gpm can be 
provided in the same room, all because the engineer doesn't accept the 
testing and listing data from the manufacturer, and has chosen to ignore 
the black and white text of the applicable standard. 

Now throw in the possible addition of 5 gpm for a domestic flow, which 
many AHJ's are requiring, and now you're potentially flowing more than 
31 gpm through the meter.  Depending on the manufacturer this might rule 
out the use of a 3/4" meter and force the homeowner into purchasing an 
upgraded meter, at a cost of thousands of dollars.  Steve Leyton can 
give you more information on that than I can, but in one water district 
here in San Diego county the difference in a 3/4" vs. a 1" water meter 
is $14,000. 

Four times the sprinklers the listing would require, larger pipe than is 
necessary, an upgraded meter, and potentially a pump.  What if the 
system were supplied from onsite storage?  Now the tank must be twice 
the size as well.

Doesn't add up to a "better" approach to residential fire protection 
from where I sit.

He's spending four times the owners money necessary [not his own, mind 
you] to provide the same level of fire protection.  Not "better", the 
same.  At four times the cost.

 From perspective of this quite humble sprinkler layout technician 
that's just wrong.
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website





Chris Cahill wrote:
> This is important - LET ME PLAY DEVIL'S ADVOCATE, where is the engineer
> WRONG?  Quick look at Tyco LF II 4.9 pendant 12' x 12' is 13 gpm.  And at
18
> gpm it's a 13.49 psi start.  The sidewalls at 4.2 will do 13gpm at 9.2 psi
> so you are not forced under a 7 psi start. So he won't let you use 16' x
20'
> spacing?  Just because one won't allow what in essence is extended
coverage
> doesn't make one ignorant. 
>
> Is this not the equivalent of not allowing sched 7 and only allowing sched
> 40 threaded noting sched 7 has many more times the CRR?  Both cases are
text
> book verse a real application.  Perhaps some think 12' x 12' spacing is
> better then EC and 40 is better than 7 when applied to a real project.
How
> often do we see a spec say no EC? How often do we see no reduction for QR?
>
> I acknowledge you did say he is reading out of the where not been listed
> with special...so his argument may be flawed but his conclusion probably
> isn't from his perspective.  I'm sure you recall the 13/18 was the
original
> NFPA 13R/D spec and the first heads had no other spacing options.  But it
> also looks like at least in Tyco's case the low end it's the same on the
> 13gpm side.  Yeah the dual gpm is gone.  But an engineer can spec any
> density greater than the minimum.     
>
> I didn't talk with the engineer perhaps he/she/it is ignorant or perhaps
> just exercising engineering prerogative like all the other times we see
it.
>
>
> Again that was the other side of the coin.  I'M ON YOUR SIDE TODD.  I
> wouldn't cost the owner extra money in what will probably be a lot of
extra
> heads but I don't see anything WRONG here. 
>
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>  
> 763-658-4483
> 763-658-4921 fax
>  
> Email: [email protected]
>  
> Mail: P.O. Box 69
>         Waverly, MN 55390
>  
> Location: 4439 Hwy 12 SW
>               Waverly, MN 55390
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, May 19, 2010 8:39 AM
> To: [email protected]
> Subject: RE: 13R sprinklers
>
> Todd ,
>  Are you saying the engineer has seen and has read these sections of 13R
and
> still doesn't understand the requirements ? If so , you may have to go
over
> his head to a higher authority or say a prayer and try to appease him as
> best you can.
>
> Good Luck ,
>
> Lamar Vaughn , SET
>
>   
> ---- Todd Williams <[email protected]> wrote: 
>   
>> Discharge - 6.7.1.1.1, Coverage - 6.7.1.3.1. NFPA 13R (2002)
>>
>>
>>
>> At 08:23 AM 5/19/2010, you wrote:
>>     
>>> I'd ask him to please, for your edification, cite the sections of 
>>> the NFPA Standard where he derived his specification data.
>>>
>>> I guess he was looking at sprinkler data sheets and when it didn't 
>>> say that the sprinkler is designed for 0.10 or whatever gpm/sq. ft 
>>> he thinks it falls into that category?
>>>
>>>
>>> Craig L. Prahl, CET
>>> Fire Protection Specialist
>>> Mechanical Department
>>> CH2MHILL
>>> Lockwood Greene
>>> 1500 International Drive
>>> Spartanburg, SC  29304-0491
>>> Direct - 864.599.4102
>>> Fax - 864.599.8439
>>> [email protected]
>>> http://www.ch2m.com
>>>
>>> -----Original Message-----
>>> From: [email protected] 
>>> [mailto:[email protected]] On Behalf Of Todd
>>>       
> Williams
>   
>>> Sent: Wednesday, May 19, 2010 6:11 AM
>>> To: [email protected]
>>> Subject: 13R sprinklers
>>>
>>> I am working on a project with a rather ignorant engineer who will
>>> not accept listed flow requirements for residential sprinklers. He is
>>> insisting on using the 12 x 12 spacing, 13 gpm for multiple sprinkler
>>> flow and 18 for single sprinkler flow (we have to calculate both). My
>>> question may be one of semantics, but this is what the engineer is
>>> hanging everything on. Both the above spacing and discharge
>>> requirements are under sections entitled "Sprinklers That Have Not
>>> Been Listed with Specific (Discharge/Coverage) Criteria". Since
>>> virtually all of the residential sprinklers I am aware of have
>>> specific design and coverage criteria, am I to assume based on the
>>> wording that sprinklers with specific criteria cannot be used under
>>> this section? If so, are there any sprinklers without specific
>>> criteria currently on the market?
>>>
>>> Todd G. Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> 860.535.2080
>>> www.fpdc.com
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>       
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>     
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to