Ron, We talked about this in the Hanging and Bracing committee. We came up with the following new section in NFPA-13,
9.2.1.3.3.4* Where flexible sprinkler hose fittings are used to connect sprinklers to branch lines in suspended ceilings, a label limiting relocation of the sprinkler shall be provided on the anchoring component. and A.9.2.1.3.3.4 An example of language for the label is as follows: CAUTION: DO NOT REMOVE THIS LABEL. Relocation of this device should only be performed by qualified and/or licensed individuals that are aware of the original system design criteria, hydraulic criteria, sprinkler head listing parameters, and knowledge of the state and local codes including NFPA 13 installation standards. Relocation of the device without this knowledge could adversely affect the performance of this fire protection and life safety system. Norm and his competitors readily agreed to this. -- PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [email protected] <mailto:[email protected]> e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website Fletcher, Ron wrote: > Even more interesting will be when the electrician, HVAC or ceiling guy > decide they can put the head back close to where it was without a sprinkler > contractor on site. > > Ron Fletcher > Aero Automatic > Phoenix, AZ > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Chris Cahill > Sent: Friday, May 28, 2010 7:45 AM > To: [email protected] > Subject: RE: Flexible Heads, a Learnable Moment > > No doubt but I'm sure it's not news you are the Kleenex and Xerox of the > industry. Probably even more so than Vic couplings. > > What will be interesting in the future is when the original installation > uses Flexheads and a retrofit company sees 'flexheads' and substitutes > another brand with significantly higher friction loss. Don't see too many > AHJ picking up on that one. > > Chris Cahill, P.E. > Fire Protection Engineer > Sentry Fire Protection, Inc. > > 763-658-4483 > 763-658-4921 fax > > Email: [email protected] > > Mail: P.O. Box 69 > Waverly, MN 55390 > > Location: 4439 Hwy 12 SW > Waverly, MN 55390 > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Norman > MacDonald > Sent: Friday, May 28, 2010 9:32 AM > To: [email protected]; [email protected] > Subject: RE: Flexible Heads, a Learnable Moment > > I would like to point out that NONE of the products depicted in the attached > website link are FlexHead products. The term flexhead is a registered > trademark of FlexHead Industries, Inc. The FlexHead product is a 1" > true-bore, fully braided and welded hose with a totally different bracketing > system. Please feel free to check out our w3ebsite or contact me directly > for additional information. > > Norman MacDonald > > > FLEXHEAD Industries, Inc. > 56 Lowland Street > Hollsiton, MA 01746 > (508) 893-9596 TEL > (508) 893-6020 FAX > [email protected] EMAIL > www.flexhead.com WEBSITE > > This e-mail, and any attachments thereto, is intended only for use by the > addressee(s) named herein and may contain legally privileged and/or > confidential information. If you are not the intended recipient of this > e-mail, you are hereby notified that any dissemination, distribution or > copying of this e-mail, and any attachments thereto, is strictly prohibited. > If you have received this e-mail in error, please immediately notify me by > return e-mail and permanently delete the original and any copy of this > e-mail message and any printout thereof. > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Brad > Sent: Friday, May 28, 2010 10:01 AM > To: [email protected] > Subject: RE: Flexible Heads, a Learnable Moment > > http://inspector911.com/ > hi 1st mentor, > others have addressed your question- I just wanted to add this about flex > head installation (inspection). > at the bottom of the 1st page of this site there is a 'Does this meet code' > thing about flex head connectors- and comments. > > Thanks Vince (35 years late), > Your 1st pain in the @$$ > > > -----Original Message----- > From: Vince Sabolik [mailto:[email protected]] > Sent: Friday, May 28, 2010 8:26 AM > To: [email protected] > Subject: Flexible Heads, a Learnable Moment > > Good morning, forum -- > > I'm curious to see how sprinkler designers here handle > flexible heads, namely how far do you set the > line and tee from the target in > in the pad. > > Do you use a flex head with a 90° - or straight ? > > > > listening.... > Vince > > > Vince Sabolik > Christi Fire Protection, Inc. > 11351 Pearl Road > Strongsville, Ohio 44136 > > T 440 572-7730 F 440 572-7719 Email: > <mailto:[email protected]>[email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)