Ron,
To address this concern, FlexHead provides tamper-resistant screws with every 
product that we sell.  We also worked hard to get language added to NFPA13's 
newest publication that requires a warning labels on every flexible product 
stating:

"Caution:
Relocation of this device should only be performed by qualified and/or licensed 
individuals that are aware of the original system design criteria, hydraulic 
criteria, sprinkler head listing perimeters, and knowledge of NFPA 13  
installation standards.  Relocation of the device without this knowledge could 
adversely affect the performance of this fire protection and life safety 
system."

Norm   


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Friday, May 28, 2010 11:02 AM
To: [email protected]
Subject: RE: Flexible Heads, a Learnable Moment

Even more interesting will be when the electrician, HVAC or ceiling guy decide 
they can put the head back close to where it was without a sprinkler contractor 
on site.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Friday, May 28, 2010 7:45 AM
To: [email protected]
Subject: RE: Flexible Heads, a Learnable Moment

No doubt but I'm sure it's not news you are the Kleenex and Xerox of the
industry.  Probably even more so than Vic couplings. 

What will be interesting in the future is when the original installation
uses Flexheads and a retrofit company sees 'flexheads' and substitutes
another brand with significantly higher friction loss.   Don't see too many
AHJ picking up on that one.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Norman
MacDonald
Sent: Friday, May 28, 2010 9:32 AM
To: [email protected]; [email protected]
Subject: RE: Flexible Heads, a Learnable Moment

I would like to point out that NONE of the products depicted in the attached
website link are FlexHead products.  The term flexhead is a registered
trademark of FlexHead Industries, Inc. The FlexHead product is a 1"
true-bore, fully braided and welded hose with a totally different bracketing
system.  Please feel free to check out our w3ebsite or contact me directly
for additional information.

Norman MacDonald

 
FLEXHEAD Industries, Inc.
56 Lowland Street
Hollsiton, MA 01746
(508) 893-9596 TEL
(508) 893-6020 FAX
[email protected]  EMAIL
www.flexhead.com  WEBSITE

This e-mail, and any attachments thereto, is intended only for use by the
addressee(s) named herein and may contain legally privileged and/or
confidential information. If you are not the intended recipient of this
e-mail, you are hereby notified that any dissemination, distribution or
copying of this e-mail, and any attachments thereto, is strictly prohibited.
If you have received this e-mail in error, please immediately notify me by
return e-mail and permanently delete the original and any copy of this
e-mail message and any printout thereof.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Friday, May 28, 2010 10:01 AM
To: [email protected]
Subject: RE: Flexible Heads, a Learnable Moment

http://inspector911.com/
hi 1st mentor,
others have addressed your question- I just wanted to add this about flex
head installation (inspection). 
at the bottom of the 1st page of this site there is a 'Does this meet code'
thing about flex head connectors- and comments.

Thanks Vince (35 years late),
Your 1st pain in the @$$


-----Original Message-----
From: Vince Sabolik [mailto:[email protected]] 
Sent: Friday, May 28, 2010 8:26 AM
To: [email protected]
Subject: Flexible Heads, a Learnable Moment

Good morning, forum --

I'm curious to see how sprinkler designers here handle
flexible heads, namely how far do you set the 
line and tee from the target in
in the pad.

Do you use a flex head with a 90° - or straight ?


 
listening.... 
Vince


Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730  F 440 572-7719  Email: 
<mailto:[email protected]>[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to